Hi Jeremy
It is late so my thoughts are not complete, but my
first thought would be to use a 3+ kW inverter and
plan to have 3 arrays of 1 kW each in parallel.  This
means you need to select modules with voltages to meet
the inverter's voltage requirement from a single 1kW
string.  You also need a combiner box that can handle
3 high voltage circuits with fusing for each circuit. 


The caution here is each string must be fused at less
than or equal to the Max series fuse size for the
modules.  If the modules can handle a 15 amp fuse then
a 600 Volt 3phase, 30 amp disconnect with 15 amp fuses
could be your combiner box.

Darryl     

--- Jeremy Rodriguez <allsolar at ris.net> wrote:

> 
> Grid Tie Wrenches,
> I have a client interested in a grid connected
> system (no batteries) 
> with the capability of expanding in three phases. Is
> there a 
> configuration that will work using a single inverter
> and installing 
> three seperate arrays 1kw each, at three different
> times. The goal is a 
> 3kw array with one inverter. I can see it happening
> with a battery based 
> inverter, correct.
> 
> New to this grid tie market!
> Jeremy
> All Solar
> 
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios:
> www.mrsharkey.com/wrenches/
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
>
> 
> 


__________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around 
http://mail.yahoo.com 


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list