deep battery discharge [RE-wrenches]

Warren Lauzon windsun at wind-sun.com
Fri Jul 28 10:14:55 EDT 2006



They probably can, but you might need a higher voltage kick start to get the electrolyte up high enough to where it will conduct again. In the past we have managed to recover SOME (not all) such situations by putting an overcharge on them, around 2.5 VPC until they start bubbling.

What often happens in such banks with series batteries is that you will have one or two that is 100% dead, and you might have to kick start it with, maybe with a direct PV to battery connection for a short while.

Under NO circumstances should you put new acid in them. I am guessing that the SG of the electrolyte right now is around 1.1 to 1.15, which is far below what most hydrometers will measure.

However, obviously, if some cells got damaged,he might be out of luck.

-------------------------------------------------------------------------
Northern Arizona Wind & Sun - Electricity From the Sun
Free Solar Discussion Forum: http://www.wind-sun.com/smf/index.php
-------------------------------------------------------------------------
  ----- Original Message ----- 
  From: Ron Young 
  To: RE-wrenches at topica.com 
  Sent: Friday, July 28, 2006 2:59 AM
  Subject: deep battery discharge [RE-wrenches]



  Hi all,
  I've got a client who inadvertently discharged his relatively new set 
  of 1900 a/h lead acid batteries (left a light on that was directly 
  wired for about three weeks). The voltage reading is 10.5v, I can't 
  even get a reading on a hydrometer so it looks like the electrolyte is 
  pretty much water. The 750 watt 12v array is only registering .4 amp in 
  bright sun -through an SB50L -is this because the batteries can't 
  accept a charge now? Are they toast or can they be recovered?

  Ron Young

  earthRight - Solareagle.com
  (250) 392-7119
  79f North Third Ave
  Williams Lake, BC
  V2G 2A3
  Canada


  - - - -
  To send a message: RE-wrenches at topica.com

  Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

  List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

  Check out participant bios: www.mrsharkey.com/wrenches/

  Hosted by Home Power magazine

  Moderator: michael.welch at homepower.com




[Non-text portions of this message have been removed]


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list