Conrad, et al ;
YES ! details --some time called proper design.
The original ABC, and many site built tanks, are first of all made of
corrosion free materials-- polyethylene,EPDM, fiberglass or flexible liners
like high quality PVC. My favorite for building large tanks in areas with
small access doors. The tanks have varied some over the years but I cover,
now seal , them enough to greatly reduce evaporation . Usually use a bronze
pump, although I have some tanks piped to steel heat exchangers in wood
stoves that have some sodium nitrate to de-oxygenate the water.

You mention overproduction issues-- something that I think of as more of a
problem with AF. Maybe that high temp vapor migrating up the return line ?
That's easy to cure with a P trap.

I'm familiar with the Acorn as I have a Navy Captain [Ret] customer on the
banks of the Potomac, a very cold, windy site, that just loves his. We will
be replacing the fiberglass glazed, black paint absorber with some
remanufactured Reynolds collectors using thermafin plates from AET before
Winter. But as new owners arrive, or roofers are needed, especially in an
area with bad experiences , they do tend to get removed. Real estate agents
don't like what they don't understand.

I wasn't interested in contractor's names--They probably left 12/31/85--
just trying to point out how a bad apple , or more , can spoil a market for
a long time.  Are you paying attention CA, NJ, etc ?

Like you, I'm not terribly worried about acidic glycol unless it's a system
that chronically overheats but manages to stay online. I rebuilt one system
that had never circulated for10 years after install. Took real persistance
to
loosen all the dried up Propylene-- I think, it sure was brown-- and get it
free to circulate. But it would hold pressure !
PV pumping does seem to be problematical for overheat protection.
By the way, for pumped systems with sensor controls, I just but a $15 'fan
on ' switch set at 175* [ adjustable, 40 * diff ] in the storage sensor line
and attached to the tank at an appropriate place, to get the pump to run at
nite for cool down. --Vacation switch--

Try the vacation switch. I'll bet you have less expansion tank failure-- air
vents too! Not to mention loss of AF thru hard to find seeps.

Those heavy tanks were why I was interested in the poly tanks to begin with
!  Although we just serviced two of those cement lined tanks today and
they're going strong.I hate taking them out more than putting them in-- have
to come up the basement steps!
Watch out for those psycho squirrels-- for a while down here they were
getting under collectors mounted 4" above shake roof and going right thru to
the attic. I wonder what they do under a PV array?

Thanks for the clarification---
Enjoy the weekend all
Ken


----- Original Message -----
From: "Conrad Geyser" <conradg at cape.com>
To: <RE-wrenches at topica.com>
Sent: Thursday, June 08, 2006 10:13 PM
Subject: Drainback vs. Closed Loop details [RE-wrenches]


>
> Ken Travis Geoff Smitty...
> Trying to fill in the details a little as Ken was asking.
> Most (not all) of my prejudice does come from small tank, vented SDHW
> drainbacks.
> Sunhouse is the only packaged name that comes to mind.
> These needed filled on a regular basis & had custom built in circulators,
> two unfortunate aspects.
> Also a few site built collector/ big tankers have had to be
de-commissioned.
> Of these Acorn House systems are a branded name.  Freeze ups & overall
> system dissatisfaction have been the downfalls.
> I work hard at trying to keep these on line, but haven't had success with
> the orphaned drainbacks.
> I'm afraid I have to balk at naming contractors, sorry Ken.
> - A retraction:  I recall two 80's drainbacks that are still going.  They
> both have small, unvented drainback tanks.
> Mea Culpa, shooting from the hip.
>
> There are many cases where a drainback is the preferred design.
> Just in regularly freezing areas, where there aren't extensive
> overproduction issues, generally, I wouldn't support drainbacks.
> Those narly glycol loops are just too hard to beat.  If something goes
> kaflooey and the glycol boils for a period of time, just change it, no
> biggie.
> Those dime a dozen cast iron circulators go for twenty years in glycol.
> The only time I've seen corrosion from bad glycol is when some psycho
> squirrel chewed a huge hole in the outlet pipe and the collectors sat and
> boiled for years afterwards.  Outwardly the collectors looked mint, but
they
> were paper thin.
> I think that it really comes down to the details.  Ken says he's got it
> worked out.  Ken, are your DB tanks vented?
> The sol-reliant design sounds like it makes sense.  Do we know that the
> glycol residue in the collectors being boiled isn't an issue?  What about
> late day non controlled PV heat dumping?
> details details
> For instance, we've had trouble with Amtrol #15 expansion tanks.  And
Vaughn
> HX tanks.  Now we don't use either.
>
> Happy heating,
> Conrad G.
> Cotuit Solar
>
>
>
> ----- Original Message -----
> From: "Ken Schaal" <ken at commonwealthsolar.com>
> To: <RE-wrenches at topica.com>
> Sent: Thursday, June 08, 2006 8:37 AM
> Subject: Re: Drainback vs. Closed Loop Circulators [RE-wrenches]
>
>
> >
> > Ahh-- how the past design failures affect form our thought patterns  [
> > prejudices?] !
> >
> > 1- If we are talking about side arm, small dB tank w/ HE, I agree that
> > control failure is a concern .  I've very rarely encountered a broken
tank
> > sensor wire to cause constant on. More likely on the collector sensor,
> > corroded connection causing delayed on, or broken, typically from ice or
> > squirrels-- buzzards once- causing no pump on.
> >
> > 2-- Large tank DB makes prolonged 'pump on ' much less critical.
> >
> > 3-- The ultimate issue is which system, overall, is more effective at
> > producing useful energy for extended years. For all our efforts, weather
> > PV
> > or SHW or Passive Design or Wind or Hydro, the devil is in the details.
> > The
> > best use of this list is to get those details RIGHT.
> >
> > 4--We never had many side arm DB's in Richmond, mostly Reynolds
> > anti-freeze
> > systems, my large tank DB, various other systems both AF and side arm
DB.
> > We
> > didn't have too many shysters to give a really bad taste ! Our climate
is
> > quite variable 0-100, cloudy to blazing sun, ice and snow . A good
> > sampling
> > of weather. We need to be efficient for a SWH to be cost effective. [
> > Large
> > tank DB tests out at 600-800 BTU's per sq ft per day annual ave.
depending
> > on the details.]
> >
> > I have many more service calls for AF than large tank DB. The only
frozen
> > collectors were when they were immediately above a very hot tank-- one
> > tied
> > into a wood fired boiler, another when the house was vacant-- which took
a
> > simple shallow P trap in the return line to keep solar tank vapor from
> > migrating into the collector.
> >
> > 5--On residential size systems filling the collectors under stagnation
> > conditions is always impressive and should not to be typical, but is
> > hardly
> > catastrophic. With a typical high head circulator, the flow is self
> > limiting
> > as soon as steam forms. At least with large tank systems with the return
> > carried below water level and appropriate vacuum break to allow
draining,
> > steam dissipates quickly. Larger systems deserve more care, but again
have
> > not been a problem in real world conditions.
> > Fortunately we now have a great control from Thermo Technologies,-- the
> > evacuated tube guys-- that gives digital control, temps, high limits for
> > bottom and top of tank , as well as collector. Also provides BTU calc.
all
> > for a $100.  Ahh, progress!  [ No. I have no financial links . Mahjouri
> > hasn't even been able to get me to try evac tubes ! I still have to many
> > flat plates from a poorly designed AF commercial system that was taken
off
> > the roof after leaking ethylene glycol onto a built up tar and gravel
> > roof.
> > 100 --4x12 's ]
> >
> > 6-- Todd's comment were right on-- very little risk, lot's of
performance
> > advantage, details matter, as well as basic system design. Remember, if
> > there is a failure mode, the water is moving and it's the whole tank,
> > which
> > has probably been at least partially heated the day before, that has to
be
> > cooled to below 32.
> >
> > OK Smitty-- let's here the bloody details. We don't want PV to get all
the
> > gory attention !
> >
> > It's all for the good of SOLAR
> >
> > Be careful out there all  -- Ken
> >
> >
> >
> > ----- Original Message -----
> > From: "Bill Loesch, Saint Louis Solar" <bill_loesch at compuserve.com>
> > To: <RE-wrenches at topica.com>
> > Sent: Thursday, June 08, 2006 3:25 AM
> > Subject: Re: Drainback vs. Closed Loop Circulators [RE-wrenches]
> >
> >
> >>
> >>
> >> I cannot agree more with Todd that using water in a freezing climate is
> >> _asking_ for a catastrophic failure at some point. Those KISS drainback
> >> folks need to keep their brazing skills in good practice in
anticipation
> > of
> >> the control failure mode.
> >>
> >> Another rarely discussed aspect of drain back is the thermal shock of
> >> pumping "cold" fluid into "hot" collectors.
> >>
> >> Bill Loesch, Solar 1- Saint Louis Solar
> >>
> >>
> >> Message text written by INTERNET:RE-wrenches at topica.com
> >> >
> >> The only caveat with drain backs is the possibility (albeit very small)
> >> of freezing. I agree with all the advantages mentioned about drainback
> >> systems versus glycol... but I do not think it wise to trust a snap
> >> switch and/ differential controller or its temp sensor to not
accidently
> >> pump water through the system during times of freezing weather. Brazing
> >> leaks on a burst absorber panel is no fun.
> >>
> >> Todd
> >>
> >> <
> >>
> >>
> >> - - - -
> >> To send a message: RE-wrenches at topica.com
> >>
> >> Archive of previous messages:
> > http://lists.topica.com/lists/RE-wrenches/read
> >>
> >> List rules & how to change your email address:
> > www.mrsharkey.com/wrenches/etiquette.php
> >>
> >> Check out participant bios: www.mrsharkey.com/wrenches/
> >>
> >> Hosted by Home Power magazine
> >>
> >> Moderator: michael.welch at homepower.com
> >>
> >>
> >
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages:
> > http://lists.topica.com/lists/RE-wrenches/read
> >
> > List rules & how to change your email address:
> > www.mrsharkey.com/wrenches/etiquette.php
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list