Drainback vs. Closed Loop Circulators [RE-wrenches]
Jeff Clearwater
clrwater at earthlink.net
Tue Jun 6 01:51:15 EDT 2006
<x-flowed>
Hey Travis,
This is excellent info! Thanks, I really appreciate the real world data!
Best,
Jeff C.
>Hello Jeff,
>
>We just did a drain back system with six 4x10 flat plates. Calculations
>showed that we had to use Grundfos 26-96 to overcome the head and total
>pressure drop. I carefully added up every foot of pipe, valve, elbow etc to
>make sure I didn't oversize it.
>
>It's rated at 215 watts but we choked the flow down to ~9 gpm (1.5 per
>panel) and dropped the wattage to 135 as measured with a Brand power meter.
>
>The pump would do almost 20 gpm with out reducing flow which was higher then
>the charts said it would do so I assume there was a siphon effect adding to
>the flow. But you can't factor that into the pump sizing as you have to
>overcome the head initially. And the next smaller pump left no room to
>safely overcome the head plus it didn't use much less wattage.
>
>I'll gladly use the extra energy to get all the benefits of drain back. In
>the morning I saw a 20f delta t at 9 gpm. Of course the Delta T drops as
>the days goes on but stays above 10. That's 90,000 BTU's of heat for 460
>BTU's worth of electricity. So the average of the day that's 1% of the
>energy collected is used to pump. Share that with the "thermal engineer"
>and see what he says.
>
>The common circulation pump is centrifugal which is not a positive
>displacement type. Very low wattage positive displacement pumps are
>available that can handle the temp but their flow rate limits them to a max
>of several panels. Ken Schaal of Commonwealth Solar can speak with direct
>knowledge of them.
>
>Best,
>
>Travis Creswell
>Ozark Energy Services
>
>
>-----Original Message-----
>From: Jeff Clearwater [mailto:clrwater at earthlink.net]
>Sent: Friday, May 19, 2006 7:56 AM
>To: RE-wrenches at topica.com
>Subject: Drainback vs. Closed Loop Circulators [RE-wrenches]
>
>
>Hi All,
>
>We have been getting back into offering Solar DHW - mostly due to two
>factors that make it a doable business model in terms of
>installation, service and liability.
>
>The first is switching to evacuated tube collectors. They are light,
>easy to ship and handle and easy to install - I don't have to worry
>about cranes or major racking weight and it eases safety factors with
>my installers.
>
>Second is going with drainback instead of closed loop glycol. This
>eliminates having to service the glycol every 2-3 years and actually
>gives a chance that the system might live on when the folks sell the
>house etc.
>
>However, I recently suggested drainback, closed loop to a low income
>zero energy home development we are working with and the thermal
>engineer came back with data saying that the drainback circulators
>used up to 1/3 of the energy harvested by the system in terms of
>electrical cost vs. gas saved! I find that hard to believe. He
>claimed the closed loop circulators use less but still was showing a
>significant percentage. I'm not sure whether he's just finding an
>excuse to go with what he is used to or whether there is a
>significant difference here.
>
>So the questions for my esteemed wrenches are:
>
>1) Does anyone have KWH use figures for solar DHW circulators?
>2) Does anyone know of the most efficient circulators? (are
>circulators positive displacement pumps?) - any models to suggest for
>drainback?
>3) Do folks recommend using PV direct pumping for drainback? What
>controller would one use then?
>
>Thanks!
>
>Jeff C.
>
>--
>~~~~~~~~~~~~~
>Jeff Clearwater
>Village Power Design
>Sustainable Energy & Water Solutions for Home & Village
>http://www.villagepower.com
>gosolar at villagepower.com
>NABCEP (tm) Certified Solar PV Installer
>
>530-470-9166
>877-SOLARVillage
>877-765-2784
>72 Baker Rd.
>Shutesbury, MA 01072
>425 Nimrod St.
>Nevada City, CA 95959
>~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address:
>www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
--
~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design
Sustainable Energy & Water Solutions for Home & Village
http://www.villagepower.com
gosolar at villagepower.com
NABCEP (tm) Certified Solar PV Installer
530-470-9166
877-SOLARVillage
877-765-2784
72 Baker Rd.
Shutesbury, MA 01072
425 Nimrod St.
Nevada City, CA 95959
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list