Hi Daryl,
I didn't want to infer that it's acceptable to remove the connection to the
ground rod--just floating a scenario (no pun intended). You are exactly
correct, its best to have all equipment tied to the grounding system.
Please note new phone extensions
---------------------------------------------------------
Phil Undercuffler
Technical Service Manager, ext. 0741
Conergy, Inc.
1730 Camino Carlos Rey Suite 103
Santa Fe NM 87507 USA
Tel 505-473-3800 ext 0741
Fax 505-473-2134
www.conergy.us
---------------------------------------------------------
-----Original Message-----
From: Darryl Thayer [mailto:daryl_solar at yahoo.com]
Sent: Tuesday, May 23, 2006 9:52 PM
To: RE-wrenches at topica.com
Subject: RE: ground rod question [RE-wrenches]
Actually Phil is correct as usual, but having recived
many a shock by being grounded and touching energized
equipment, I prefer to have the equipment connected to
a ground rod ALSO. A seperate structure does not have
to have a bonding jumper back to the main service.
However I prefer to use one.
One thing that is needed in these cases is a grounding
system, i.e. a ground rod and other ground means. In
the case of a pole mount the foundation (when set up
as a Uffer ground) and a ground rod can fullfill
these requirments. Having two ground points will
allow them to be connected and a ground test can be
made on this arraingment. I have measured less than
0.1 ohms between ground rods, and of course as high as
3000 ohms.
Thanks Phil for correcting and making these
installations safer.
darryl
--- Phil Undercuffler <p.undercuffler at conergy.us>
wrote:
>
> Darryl Thayer said <snip>
> As I see it the ground rod on a PV array is for two
> purposes, .... Two to
> protect grounded people from any errant
> voltages/currents that they might
> contact during fault conditons. (part two is what
> the electrical inspector
> is looking for).....
>
> Actually, this is one function the ground rod does
> NOT perform. The bonded
> conductor (neutral or negative, generally) provides
> the return current path
> for any fault current, which trips the fuse or
> breaker thereby clearing the
> fault.
>
> If you make a short between hot to ground (Please
> don't attempt this at
> home), the breaker will trip no matter whether the
> ground rod is connected
> or not. However, if you remove the bond between the
> grounded conductor and
> the equipment ground, the breaker won't trip no
> matter how many ground rods
> you drive, thereby presenting potential voltage
> hazards to your grounded
> people--and we all know how hard it is to find well
> grounded people
> sometimes, so you don't want to waste them ;-)
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
See the hottest games before your friends! Sign up with Ubisoft,
and you'll get access to exclusive game news, contests, promotions,
community forums, and more. It's easy, free, and secure.
http://click.topica.com/caaePuxbz8Qcsbz9JC9f/ Ubisoft
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com