The OutBack FX series inverter's gen start system gives a 12vdc output - 
not a relay (switch) closure when it signals the generator to run.  A 
small 12vdc coil relay is required to provide the circuit "closure" to 
signal the Kohler to run.  

We used a separate relay because there where too many times we saw a 
complete SW series inverters coming back for repair because someone 
hooked up the genstart relay incorrectly and had the full starter 
current go through it.  With a separate relay its easy to replace in the 
field if a mistake is made.  

Also - thanks Jay for pointing out that the MATE does include quiet time 
- in fact you can set the quiet time different on weekends than weekdays 
with the OutBack gen management system.  

The Kohler just needs a connection of the start (RUN) terminal to 
battery negative in order to run.  Since the battery negative is 
connected to the chassis of the generator (like in a car) the term 
"ground" is used.  I have seen this result in ground faults more than 
once - so be sure to watch how the generator is wired up...  

Christopher

David Palumbo wrote:

> For my education - you said to use a 12v relay (which I understand is
> usually used so the Aux dry contacts on the OB do not want to see any
> current) then you say "but the Kohler is ground started". Does this but 
> mean
> that we really don't need the 12v relay in this start circuit because 
> there
> is no current? I'm unclear as to the necessity of the 12v relay in this
> case. DP
> 
> << You will only need a 12v relay as the contacts from the FX are 12
> powered, but the Kohler is ground started.  So just connect the relay
> to close on command from the aux relay and hook up the NO contacts to
> the genny and you are set to go. >> Jay
> 
> jay
> 
> peltz power
> On May 12, 2006, at 5:48 AM, David Palumbo, Independent Power & Light
> wrote:
> 
> >
> >
> > What part(s) do I need to add to a basic Out Back off grid pv
> > system for
> > automatic gen start/stop? Must include a clock prohibiting gen run
> > during
> > overnight (the old Trace SW quiet time).
> >
> > Client just received a brand new two wire start Kohler LP 8.5k
> > (8.5RES)generator. As far as I can see the OB FX2524T and Mate do
> > not have a
> > quiet time in their program.
> >
> > Would any of the after market gen control products help with this?
> > Such as
> > Solar Converters GS2, or GSCM's control module?
> >
> > Thanks for your help,
> >
> > Dave
> >
> >
> >
> 
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages: 
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios: www.mrsharkey.com/wrenches/
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
> 



Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com  
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030  


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list