Replacing overflowed electrolyte (was: More on battery management) [RE-wren
Bob Ellison
ellison at gisco.net
Wed May 10 19:41:09 EDT 2006
Another way to do this is somewhat dangerous, it is called acid balancing. I
have to do it a couple times a year when some ID10T overflows the battery
cells. Get some 1.400 grade acid, Measure all the cells with a hydrometer,
remove electrolyte from the low cells to the top of the plates depending how
diluted they are. Then add 1.400 to the full ring. Charge all batteries
until the electrolyte is well mixed. Measure gravity again. If still low
remove more electrolyte and add more 1.400 and redo the process. If you go
over remove electrolyte and add a small amount of water and repeat the
process till you get it right.
I maintain several industrial batteries, 40 cells each and 80 volts. These
puppies will shock you if you get between the hot and case or ground. How
much depends on where in the string you are making contact.
If the batteries have the flip top caps the fill pitcher will overfill them
every time. The caps have to be off to get the level correct.
It will be easier and safer to take the batteries to an industrial battery
shop (anyone who works on fork lift type batteries) and ask them to "acid
balance" the battery.
I don't suppose they are close enough that I could help? I have 15 gallons
or so of 1.400 sitting here looking for some cells to hang out in.....
Hope this helps,
Bob
-----Original Message-----
From: Windy Dankoff [mailto:windydankoff at mac.com]
Sent: Wednesday, May 10, 2006 4:07 PM
To: RE-wrenches at topica.com
Subject: Replacing overflowed electrolyte (was: More on battery management)
[RE-wrenches
Kelly,
Kelly, Too late for your Deka customer, but using an automotive battery
filling pitcher would probably eliminate the overfill. Plus, have customer
put it on calendar to fill only every 6 months (or whatever you judge) and
never when state-of-charge is low. Emphasize that there is no danger in
having a low level, as long as plates are submerged.
Once electrolyte has been lost due to overflow or spillage, it must be
replaced with new electrolyte, not water, or dilution will occur.
Unfortunately, your customer now has an unpleasant task to perform, based
largely on guesswork, to suck out dilute solution and replace it with
full-strength electrolyte, little by little, until finally the cells
approach some sort of correction. Yuck! This could take 2 years.
You might call Deka and propose this -- If batteries are <1 year old, there
should be practically no sediment. This makes it safe (for the
batteries) to be tipped over and emptied, then refilled with fresh
electrolyte. It would be the only way to quickly correct the situation if
the cells are now uneven.
Windy
> From: Kelly Larson <solarwrench at asis.com>
> Subject: RE: More on battery management
>
> Hi Windy and all. Thanks for sharing your battery wisdom.
>
> My questions mostly center around the batteries I install and am
> looking to maintain/coach the customer to maintain. They all start in
> new condition, I check voltage and sg on installation.
>
> I have one pack of Deka L-16 that came with one cell bad. Returned
> that bat and have been monitoring the rest. Customer took me too
> serious about keeping the batteries watered, and overwatered. Bats
> equalized
> with some electrolyte spirting out 3 or 4 times, (over 6 months).
> Then
> sg is low in all, even at full charge. I jumped to the conclusion
> that electrolyte is weak, but on investigation gathered that is
> difficult to do. Cells continue to be low and somewhat uneven after a
> year of use.
> Customer doesn't dip far into the pack, ususally only 10%, and reaches
> down to 48.5 on occasion , maybe 5 times, when he turns on the genny
> right away and gets the pack up to 90-95%.
>
> The obvious stuff, batteries swollen or on last gasp, I can handle.
> It is the more subtle problems I struggle with...and remediation on
> starting-to-go-off-the-right-path banks.
>
> Kelly Larson
> BSEE
> Ca Electrical Contractor #868189
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list