more MX60 / generator charging [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Wed Apr 26 18:19:24 EDT 2006
CVSOLAR at aol.com wrote:
>
> I think that once you are buying two MX 60's and two X240's to
> charge from a larger generator, it starts to look like just adding
> and FX inverter for battery charging might be a lot easier.
If the system already has a MX60 in it for the PV array then this might
be a good option to increase the charge rate from the generator. A
X-240 is about 1/2 the cost of the MX60 and only 1/8 the cost of another
inverter.
Just be careful with using a non-isolated autotransformer like the X-240
as it is possible to get a ground fault which would trip the PV-GFP.