A backfed circuit breaker on the distribution bus would ADD to the
possible loading of the bus. For example, 200 amp main breaker source
feeding the bus, plus a 50 amp PV source feeding the same bus would
allow 250 amps of loading which could exceed the ampacity rating of the
distribution bus.
A tap source between the main disconnect would SUBTRACT from the current
flowing. Say there is 200 amps of load down stream from the main circuit
breaker. Adding a 50 amp backfeed would reduce the current flowing from
the grid to 150 amps.
The issue is the distribution bus downstream from the main disconnect
since sources are additive there. At the same time they are subtractive
on the the meter socket or incoming service drop.
Todd
Bob Ellison wrote:
>This is an area I don't normally get into, but wouldn't a clamp onto a
>buss bar just contribute to the load on the buss bar like using a
>breaker adds to the load?
>
>Just getting confused, ( not hard on many day's
>Bob
>
>-----Original Message-----
>From: Kurt Albershardt [mailto:info at es-ee.com]
>Sent: Thursday, January 19, 2006 8:47 PM
>To: RE-wrenches at topica.com
>Subject: Re: bus bar clamps (was: calculation) [RE-wrenches]
>
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Jumpstart your love life at AmericanSinglesR.com.
>Meet someone in your area today. Millions of member profiles.
>Create a profile, post photos and search for free.
>http://click.topica.com/caaemrrbz8QcsbfmDywa/Spark Network
>-------------------------------------------------------------------
>
>--On Thursday, January 19, 2006 5:30 PM -0800 "Todd Cory, Mt. Shasta
>Energy Services" <toddcory at finestplanet.com> wrote:
>
>
>>John Berdner wrote:
>>
>>
>>
>>>I have heard about some taps designed to clamp directly onto the bus
>>>bars but have yet to find a part number or manufacturer. Any
>>>suggestions out there ?
>>>
>>>
>>Yes, this is a good thing to research. Does anyone know of a clamp
>>device to tap a busbar?
>>
>>
>
>
>T&B makes one for ground leads. I have seen others for current-carrying
>conductors but it was a long time ago and I didn't ask who the
>manufacturer was.
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Jumpstart your love life at AmericanSinglesR.com.
>Meet someone in your area today. Millions of member profiles.
>Create a profile, post photos and search for free.
>http://click.topica.com/caaemrrbz8QcsbAfWTrf/Spark Network
>-------------------------------------------------------------------
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
>
>
>
>
>
>
--
Todd Cory
KE6SXS
toddcory at finestplanet.com
Mt. Shasta Energy Services
License C-10 # 811428
P.O. Box 689
Mt. Shasta, CA. 96067
(530) 926-1079
http://www.lifeaftertheoilcrash.net/
"To announce that there must be no criticism of the president,
or that we are to stand by the president, right or wrong, is
not only unpatriotic and servile, but also treasonable to
the American public." - Theodore Roosevelt, 1918
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Jumpstart your love life at AmericanSinglesR.com.
Meet someone in your area today. Millions of member profiles.
Create a profile, post photos and search for free.
http://click.topica.com/caaemrrbz8Qcsbz9JC9f/Spark Network
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list