Paralleling Battery Banks [RE-wrenches]

Hugh Piggott hugh at scoraigwind.co.uk
Sun Dec 31 03:02:57 EST 2006


<x-flowed>

At 8:50 am -0800 30/12/06, Kurt Albershardt wrote:

>If possible, put a suitably rated fuse on each battery bank (ideally 
>as close to the battery as possible) to protect the battery cables. 
>This will prevent a short in one battery pack from taking down they 
>system and/or damaging the other battery bank.  If you use pull out 
>fuse holders, it will also facilitate battery maintenance.
>
>

Take care that pulling a fuse will not leave the charging sources 
connected to the inverter and controls without any battery.  I would 
use a separate fuse(s) for any charging sources, so that this is not 
possible.  A wind or hydro turbine that shares a fuse with the 
inverter can be a source of dangerously high voltage if the fuse is 
pulled.  Charge controllers may or may not be able to deal with the 
turbine output in the absence of batteries.  I am not sure about PV 
but I would imagine that the same problem would arise to a lesser 
extent (lower open circuit voltage).

I guess if you put a separate inverter fuse on each battery string, 
then you need multiple fuses for the charging sources as well.  Or 
else place a conspicuous sign indicating the dangers of pulling out 
all the battery fuses.
-- 
Hugh

Scoraig Wind Electric
http://www.scoraigwind.co.uk/


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list