Utility meter questioned [RE-wrenches]
William Miller
wrmiller at charter.net
Tue Dec 5 11:18:47 EST 2006
<x-flowed>
Colleagues:
We recently installed a 30 KW system on a manufacturing facility. The
customer just received the first utility bill since the system was
energized. The bill shows no savings on the electric bill.
The electronic utility meter screen 99 is reported to show instantaneous
consumption or generation into the grid. I read the meter screen 99 at
between .64 and 2.0 KW. Each of the 6 inverters were putting out about 2.0
KW each. When operating, the inverters were putting 28 amps back into the
grid on each phase.
I then shut down the inverters and the meter reading 99 did not
change. This is especially surprising in light of the fact that the plant
was in operation with all three sublimation machines and the complete line.
I will meet with the utility to see if there is indeed a problem with the
meter. In the meantime, has anyone had any experience like this?
Thanks for your thoughts.
William Miller
__________________________________________________________________
William Miller
Miller Power and Communications
Voice :805-438-5600 Fax: 805-438-4607
email: wrmiller at mpandc.com
http://mpandc.com
License No. C-10-773985
_____________________________________________________________
Check out our latest project at
http://mpandc.com/case_studies/pv_school/pv_school.html
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list