AGM battery strings: Problems? [RE-wrenches]
Kelly Keilwitz
kelly at whidbeysunwind.com
Fri Dec 1 07:54:44 EST 2006
Jim,
I know problems are possible, but was hoping that the voltage/resistance of
the two strings will be alike enough that the problems would be minimal.
What's the worse case - that the capacity of the larger string falls to that
of the smaller? We might be willing to put up with that. Or, is premature
failure a real possibility?
This is a grid-tie, hands-off, will-work-automatically-guaranteed, backup
system. So, switching between banks for won't work here.
On 11/30/06 1:02 PM, "Jim Easton" <jim at altenertec.com> wrote:
>
> Possibility of problems? Yes.
>
> Paralleling batteries of dissimilar type/history can lead to premature
> failure & lack of anticipated capacity.
>
> A better solution might be to use an A-B switch with a battery isolator for
> charging.
>
> Jim Easton
> Alternative Energy Technologies
> CSL: 852243
> 9465-B Mission Park Place
> Santee, CA 92071
> Tel: 619-262-8800
> Fax: 619-562-8811
> Cell: 858-527-0240
>
> -----Original Message-----
> From: Kelly Keilwitz [mailto:kelly at whidbeysunwind.com]
> Sent: Thursday, November 30, 2006 8:20 AM
> To: RE Wrenches listserve
> Subject: AGM battery strings [RE-wrenches]
>
>
> Wrenches,
> Recent grid outages here have a few of our grid-connected, battery-based
> customers wanting more battery capacity. Two of the systems have Concorde
> AGM's in single, 48-volt strings. I'd like to take the 2-mo old, 104AH
> (24-hr) set from one system and add it to the 6-mo old, 89AH set in another
> system.
> Do you see any problems with paralleling these different capacity strings?
> Should I cable individually from each string (2+ & 2-), or will simple,
> reverse return (1+ & 1-) flow be sufficient?
>
> Thanks,
> -Kelly
>
>
> Kelly Keilwitz, P.E.
> Whidbey Sun & Wind, LLC
> Renewable Energy Systems
> NABCEP Certified PV Installer
> 987 Wanamaker Rd,
> Coupeville, WA 98239
> PH & FAX 360-678-7131
> sunwind at whidbeysunwind.com
>
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
Kelly Keilwitz, P.E.
Whidbey Sun & Wind, LLC
Renewable Energy Systems
NABCEP Certified PV Installer
987 Wanamaker Rd,
Coupeville, WA 98239
PH & FAX 360-678-7131
sunwind at whidbeysunwind.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list