Christopher,
Can you help clarify an issue that arose during a John Wiles training
yesterday?
Are the OBDC, OBAC and OBPV breakers rated for 100% duty cycle >>>as mounted
in their enclosures? <<< (emphasis added)
John mentioned numerous times the âthermal heating effectâ of multiple
breakers when mounted in their enclosure require de-rating the capacity of a
breaker, to 80%. We are all familiar with the âyou canât run something at
100% unless the manufacturer says you canâ 80% de-rate. However, he
specifically questioned whether the OutBack breakers had been tested and
listed to maintain their 100% rating if mounted in an enclosure.
My memory is that CBI breakers have a hydraulic-magnetic trip mechanism,
which is not affected by thermal effects. Is this true, and if so, is it
true of both the OBAC and OBPV breakers? What about the OBDC, which are
made by a different manufacturer? Finally, does it apply if the breakers
are installed in a fully loaded enclosure?
We appreciate the clarification.
Phil Undercuffler
Technical Service Manager, ext. 0741
Conergy, Inc.
1730 Camino Carlos Rey Suite 103
Santa Fe NMÂ 87507 USA
Tel 505-473-3800 ext 0741
Fax 505-473-3830
www.conergy.us
---------------------------------------------------------
Â
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list