Hi Steve,

Yes, check with the service entrance panel engineers - they can 
sometimes write a letter rating the bus bar a bit higher than the 
panel rating and they can guide you on how to tap into the bus itself 
like William says.  You can also explore changing out the bus bars 
for ones of higher rating that will fit in the same panel.

Hope that helps!

Jeff C.
Village Power Design



>Steve:
>
>Are there any extra holes in the buss bars at the main?  We have 
>bolted on to the buss bars successfully before.
>
>William Miller
>
>
>At 12:29 PM 10/27/2006, you wrote:
>
>>How are people dealing with this in California?
>>If your 800 amp service is underground and the meter is on the padmount
>>transformer and the panel is in the middle of the building what do you
>>do?
>>
>>Tap into a few measley inches of 500 MCM before it hits the bottom fed
>>main?  Either that or replace the 800 amp with a 1000 amp panel?
>>
>>Lousy options if you ask me.
>>
>>Maybe people are just setting their breaker and ignoring it.
>>
>>
>>Steve Johnson
>>LightWave Electric
>>Nashville, Tennessee
>>
>>
>>- - - -
>>To send a message: RE-wrenches at topica.com
>>
>>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>>
>>List rules & how to change your email address: 
>>www.mrsharkey.com/wrenches/etiquette.php
>>
>>Check out participant bios: www.mrsharkey.com/wrenches/
>>
>>Hosted by Home Power magazine
>>
>>Moderator: michael.welch at homepower.com
>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address: 
>www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com


-- 
~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design
Sustainable Energy & Water Solutions for Home & Village
http://www.villagepower.com
gosolar at villagepower.com
NABCEP (tm) Certified Solar PV Installer

530-470-9166
877-SOLARVillage
877-765-2784
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list