690-64 (2)(B) [RE-wrenches]

Steve Johnson stevejohnson at comcast.net
Wed Oct 25 17:24:54 EDT 2006


One word. Onerous.

I have two situations but will just bring up one here.

Commercial building with 600 amp, 208 volt , 3 phase service.
Main is in middle of building in shallow double door closet, fed 
underground.  Conduit comes up on outside of building and goes straight 
to riser which is metered through rack mounted CT's.

12kw on roof feeding two 6000 kw inverters.
these inverters are protected by 40 amp 2 pole breakers.

I want to tap after the CT's and set a 100 amp panel which will have the 
two 40/2 breakers in it.  These two breakers serve as the service 
disconnect for the main by the 6 handle rule. There is no load in this 
panel.

Question is should this panel have a 200 amp bus and a 100 amp main?

Or is it ok as is.

I know someone will say load can be added.  That's fine as long as not 
more than six hand throws are required to disoconnect the service.  
(that's my story and I'm stickin' with it).


Steve Johnson
LightWave Electric
Nashville, Tennessee


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list