Bob,
Jeff's advice is good, but I may have a way to simplify (!)
IF the batteries were all used in a pack, they have identical
histories and should all be nearly equal in characteristics. If they
are not, then that is a sure sign that the weaker ones are ready to
drop out and they should not be trusted.
Therefore, I would charge and test them in series strings (no
parallel). During periods when current is high (charge or discharge),
measure voltage. If there are more than very slight discrepencies
(after a full fiinish charge) you have some weak ones and I wouldn't
trust the whole batch.
If you find enough inequalities to conclude that they aren't very
good but you wish to use them anyway -- say for a temporary setup or
a poverty-case customer, do not, repeat DO NOT parallel any strings.
If any cells short in one set, it will cause the other cells in that
string to overcharge continuously. I had this exact circumstance once
and it blew out very foul, presumably toxic vapors from the cell
vents. The customer's wife was so upset that I lost the customer. I
thought I was doing them a favor by practically giving them a
temporary battery to get them started.
And certainly have the batteries in a safely-vented environment.
Windy
> Thanks, Jeff. Note, however, that, because these are sealed
> batteries, I will be unable to measure SG.
>
> Bob Clark
> SolarWind Energy Systems, LLC
> bclark at solar-wind.us<mailto:bclark at solar-wind.us>
> ----- Original Message -----
> From: Jeff Clearwater<mailto:clrwater at earthlink.net>
> To: RE-wrenches at topica.com<mailto:RE-wrenches at topica.com>
> Sent: Friday, October 20, 2006 8:59 PM
> Subject: Re: Just how good are those used, sealed lead-acid
> batteries? [RE-wrenches]
>
>
>
> HI Bob,
>
> Here's how you do it.
>
> First understand lead acid chemistry thoroughly by reading "Battery
> Book One" by Curtis instruments or some such book.
>
> Then do the following procedure.
>
> 1) Set up a charging station for each battery separately (not in any
> series and/or parallel arrangement). ....................
--
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list