busbar overload with a GVFX-3648 is NOT a reality [RE-wrenches]
Todd Cory, Mt. Shasta Energy Services
toddcory at finestplanet.com
Fri Oct 20 14:43:44 EDT 2006
<x-flowed>
IMO reality needs to be considered. The sum of all sources can't exceed
120% of the busbar rating (NEC 690.64b(2)) of the panel.120% of 200A is
240A. With a 200A main breaker, you can also have up to a 40A inverter
feed. A GVFX3648 is only capable of a continuous supply of 30 amps.
My math shows 30 amps as less than 40 amps... yes, it is fed with a 60
amp breaker with a bi-directional current flow. 60 amp is load not
supply. Supply is 30.
The REALITY is a GVFX-3648 is INCAPABLE of damaging a 200 amp busbar in
the highly unlikely event there were 230 amps flowing through it... so
what the heck is the stink all about here???
Todd
Jeff Oldham wrote:
>Hey Wrenches, why do you have so much resistance to line taps placed between the meter and main breaker? This is so easy and cheap and takes very little time, although I don't care for them, there are even self-piercing taps that you don't even need to break any connections for or have a service disconnect to install.
>Personally, I would never down size a main breaker (and thus my customers service size) to get around the simple fix above.
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list