Andrew,
No, 175A. If it's a 200A panel, you can't put a main breaker larger than
that in it. 200A is the busbar rating of the panel - but check the label:
you might have a panel with a 200A main breaker and a higher busbar rating -
then you're OK.

Check out NEC 690.64b(2). It's the sum of all sources that can't exceed 120%
of the busbar rating of the panel. In your case, 120% of 200A is 240A. With
a 200A main breaker, you can also have a 40A inverter feed. If you put in a
60A, that would be 130%. Put in a 175A main breaker, and 175 + 60 = 235A,
which is within 120%.

Allan

----- Original Message ----- 
From: "Andrew Truitt" <atruitt at gmail.com>
>
> Do you mean 275A?
>
> On 10/11/06, Allan Sindelar <allan at positiveenergysolar.com> wrote:
> >
> > Andrew,
> > Nope, if it has a 200A main breaker; 40A is all you get. If you put in a
> > 175A main breaker, OK.
> > Allan
> >
> > ----- Original Message -----
> > From: "Andrew Truitt" <atruitt at gmail.com>
> > >
> > > Is it legit to backfeed a 200 amp main panel with the 1 pole, 60 amp
> > > breaker that is recommended for the Outback FXGT 3048 considering the
> > > 20% rule?  I know that most of that amperage is pass through, as the
> > > most a 3kW inverter should be able to produce at 120V is 25 amps, but
> > > the manual says that the largest instantaneous output current is 70
> > > amps.


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list