Backfeeding a 200 amp panel with an Outback 3048 [RE-wrenches]

Andrew Truitt atruitt at gmail.com
Wed Oct 11 13:48:24 EDT 2006


<x-flowed>

Is it legit to backfeed a 200 amp main panel with the 1 pole, 60 amp
breaker that is recommended for the Outback FXGT 3048 considering the
20% rule?  I know that most of that amperage is pass through, as the
most a 3kW inverter should be able to produce at 120V is 25 amps, but
the manual says that the largest instantaneous output current is 70
amps.

-- 
Andrew Truitt
System Designer
Standard Solar Inc.
(301) 296 - 4373
andrewtruitt at standardsolar.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/