Tri-Metric program question [RE-wrenches]
Allan Sindelar
allan at positiveenergysolar.com
Mon Oct 9 16:05:54 EDT 2006
Wrenches,
We have been including a Tri-Metric monitor with our Outback
grid-tie-with-battery-backup systems, so that the homeowner has some sort of
state-of-charge indication during an outage. We have learned to be selective
about whether to include a Mate as well, as it's not as user-friendly for
our typical non-technical grid-tie customer.
The issue is that the Tri-Met is fundamentally designed for off-grid use,
and uses charged-voltage and charged-current parameters to reset the monitor
on a regular basis. As the PS1 keeps the batteries in float, the Tri-Met can
develop an accumulated error that is only reset after a grid outage and
recharge cycle, which could be months at a time. We have seen this happen,
where the % of full slowly drifts down over days or weeks.
I called Ralph Heise about this, and he had suggestions, but no clear
answers - in fact he is looking for ideas that have worked too. He suggested
the following two ideas, which make sense in theory:
1. Set the charged voltage parameter below the float voltage (far enough
below to accommodate the effect of hot-weather temperature compensation -
say 52.4V if float is at 53.6 - and set the charged current setpoint just
above the float current - 1 or 2A, I would guess. This keeps the monitor
reading 100% while in float, and the combination of voltage and current
settings would prevent premature resetting based on voltage-above-float
alone.
2. Set the charge efficiency factor unrealistically high - say at 100% - so
that this keeps the % reading at 100% while in float. This would make the %
reading slightly high during outage cycling, but it could be easily reset
each charge cycle.
Has any Wrench out there come up with a good solution? How would you set up
a TriMet for this application? Or otherwise, how do you address the bigger
issue of a monitor that is used only during an outage?
Thanks in advance,
Allan at Positive Energy
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list