battery box venting flow rate? [RE-wrenches]
Bill Brooks
bill at brooksolar.com
Tue Sep 19 22:56:16 EDT 2006
Wrenches,
The real issue is how the local inspector will view the installation. I'm
not sure why John would say it does not have to vent to the outside, but I
definitely recommend that it vent to the outside. My basic recommendation is
that the ventilation requirements for an indoor residential battery box use
the same requirements for a gas water heater. This provides many times the
required ventilation, but it is something the inspector can readily relate
to.
Venting a battery box within a house is not a good idea. There are no
ventilation requirements for house ventilation and the natural ventilation
of house could vary from 2 air changes per hour to zero. If it happens to be
zero when the battery goes, you're in big trouble. Most commercial buildings
are required to have a 10% fresh air makeup, so venting to the room
(computer room) is not an issue when you are using AGM VRLA batteries.
So, use the ventilation requirements for a gas water heater and you're good
to go. Otherwise, spend a few thousand dollars and hire an engineer to
calculate the number of hydrogen atoms on the head of a pin.
Bill.
-----Original Message-----
From: Ray Walters [mailto:walters at taosnet.com]
Sent: Tuesday, September 19, 2006 5:38 PM
To: RE-wrenches at topica.com
Subject: Re: battery box venting flow rate? [RE-wrenches]
Well according to John Wiles's On Line course, we're not supposed to
vent batteries to the outside at all, just make sure the room they're in
is adequately ventilated.
Personally, I always liked the idea of directing the corrosive and/ or
explosive gases away from the electronics. Maybe I didn't quite get what
he was saying.
Ray
Allan Sindelar wrote:
>Kirk,
>No, because there are too many variables: battery type, age, capacity,
>temperature and condition; charge rates from different sources;
>controller/inverter settings; vent ducting; box sealing -- jeez, can I
>think of a few more?
>
>We have simply relied on Zephyr's Power Vent recommendations.
>
>Now watch me be proven totally wrong here.
>
>Allan at Positive Energy
>
>
>----- Original Message -----
>From: "Kirk Herander" <kirk at vtsolar.com>
>
>
>>Is there any minimum airflow/cfm recommended to safely power vent a
>>battery box?
>>
>>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list