Hi all. Has anyone run into Article 690.64 being interpreted as
prohibiting taps to the load side of the main service breaker? One
particular municipality is saying that, even with a fused AC disconnect,
taps are not allowed because of Item B (1) which says "Each source
interconnection shall be made at a dedicated circuit breaker or fusible
disconnecting means."
The only issue that occurs to me is the protection of the section of
wire between the tap and the fuse in the AC disconnect. Would it seem
reasonable to size that section of wire equivalent to the service
conductors?
Has anybody else run into this? How have you handled it?
The municipality in question suggests tapping on the supply side of the
main breaker, but that seems much less safe. The current on the wire
between the fused AC disconnect and the tap then only be limited by the
overcurrent protection on the utility transformer, no?
Thanks for you help.
Bruce
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list