Kaneka GSA? [RE-wrenches]

Bill Brooks bill at brooksolar.com
Wed Aug 23 12:22:11 EDT 2006


Brian,

I'm not clear on why you can't put 3 strings on an H361 (not HU361--"U"
stands for unfused) into a single inverter. You could also put 6 Kaneka
strings on a single inverter as well using the 3 or 3.5 amp IDSR fuse. As
you point out, it is the only 600Vdc Square D switch that is listed for
double lugging so you can use it as a combiner by daisy chaining the output
of the switch as long as the total current is within the rating of the lugs.

Bill.


-----Original Message-----
From: Brian Teitelbaum [mailto:brian at aeesolar.com] 
Sent: Tuesday, August 22, 2006 10:57 PM
To: RE-wrenches at topica.com
Subject: RE: Kaneka GSA? [RE-wrenches]



Doug,

Just to clarify:

If I'm reading the Square-D spec sheet correctly, the HU361RB fused switch
is not UL rated to act as a combiner for output to a single inverter, so it
can't be used to "combine" three strings. The lugs are rated to accept two
#12 or #10 wires, so you can combine two strings per pole, but each pole has
to output to separate inverters, not to one inverter. The fused version is
also only rated to carry 80% of it's rating (the non-fusible unit is rated
at 100% duty)

Here's a link to the Square-D HU361RB white paper:

http://www.sma-america.com/ftp/Square%20D%20HU361RB.pdf

The SMA Combi-Switch comes with 10A fuses, and larger fuses are not allowed.
This means that when using modules with an SC amp rating of more then 6.4A
(10A divided by 1.56 = 6.41A) you have to use a separate combiner. This
wouldn't be an issue with the Kaneka module, but since this module is only
60W, you will likely have more then four strings anyway.



Brian Teitelbaum
AEE Solar


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------









More information about the RE-Wrenches mailing list