Kaneka GSA? [RE-wrenches]

Bill Brooks bill at brooksolar.com
Wed Aug 16 17:04:26 EDT 2006


So Matt,

What would the appropriate fuse rating be for two series strings in
parallel? 

Assuming the Isc is 1 amp, then Imax = 1 amp x 1.25 = 1.25 amp [690.8(A)].

Therefore you must subtract the 1.25 amps from the 5 amp rating so the max
fuse rating is 3.75 amps

Two strings in parallel have a max current of 2.5 amps (1.25 x 2), and the
minimum series fuse rating is 2.5 amps x 1.25 = 3.1 amps [690.8(B)]. So the
correct number is 3.5 amps.

The only fuse allowable for this arrangement of two strings in parallel is a
3.5 amp fuse. I'd be interested to see if they have this in their
literature.

Bill.


-----Original Message-----
From: Matt Tritt [mailto:solarone at charter.net] 
Sent: Tuesday, August 15, 2006 8:55 AM
To: RE-wrenches at topica.com
Cc: Travis Creswell, Ozark Solar
Subject: Re: Kaneka GSA? [RE-wrenches]



-Hi Travis,

The panel label info. trumps the manual info, so that would be 5 amps. The
actual output from a series string is about 1 amp and they are designed to
be fused for 2 parallel strings with a single fuse.

Matt T
DC Power Systems


--- "Travis Creswell wrote: 
> 
> Can someone tell me what the "series fuse" rating of the Kaneka 60 
> watt module is?
> 
> Any comments on this module would be welcome.
> 
> Thanks in advance,
> 
> Travis Creswell
> Ozark Energy Services
> www.ozarkenergyservices.com
> 
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages: 
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address: 
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios: www.mrsharkey.com/wrenches/
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
>


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------







More information about the RE-Wrenches mailing list