Post Main Point of Connection [RE-wrenches]

William Miller wrmiller at charter.net
Tue Aug 8 10:50:30 EDT 2006


<x-flowed>

Colleagues:

We are installing a 30 KW system in California.  Being a commercial 
property, we are not allowed the 20% bus over rating allowed on a 
residence.  Therefore, we must connect prior to the service disconnecting 
means as allowed in NEC 690.64(A).

The utility (PG&E) is allowing this but has disallowed us from connecting 
in the same cabinet as the metering current transformers.  The next cabinet 
downstream is the service disconnect.  The switch has arc chutes in this 
section of the cabinet occupy the entire cabinet, not giving us room to 
attach to the bus bars.

Has anyone else experienced this scenario?  IF so, how have you dealt with it?

Thanks,

William Miller



__________________________________________________________________
William Miller
Miller Power and Communications
Voice :805-438-5600     Fax: 805-438-4607
email: wrmiller at mpandc.com
http://mpandc.com
License No. C-10-773985
_____________________________________________________________
Check out our latest project at 
http://mpandc.com/case_studies/pv_school/pv_school.html  


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




</x-flowed>


More information about the RE-Wrenches mailing list