Installing higher voltage array grid tie system.  Normally we route from fused array combiner to inverter down outside wall to exterior dis-connect (no fuses), then to interior inverter(s).   Client's architect vetoed exterior conduit and wants to route through roof and down inside exterior wall to above described exterior dis-connects at ground level.

We have been designing to 2005 code although this county still using older code.  New section 690.31 (E)  "Where direct-current pv output circuits are run inside a building, they shall be contained in metallic raceways from point of penetration to first accessible dis-connect."

also,

Section 690.14 (C) 5. Grouping. "The pv dis-connecting meansshall be grouped other dis-connecting means....."

Question - Does this require Intermediate Threaded Metal Conduit or is EMT allowed? How about conduit above roof line?

Question - I think inspector may ask us to move the DC array dis-connect from back of house to side where meter base and AC dis-connect are located due to above.  Does this mean up to 6 array dis-connects shall be grouped together, or ALL power source dis-connects to house grouped together?

Thanks,
Jeff Yago




_____________________________________________________________
Netscape.  Just the Net You Need.


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list