Powering a critical load sub-panel [RE-wrenches]
David Katz
david at aeesolar.com
Thu Nov 17 11:13:03 EST 2005
<x-flowed>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Is your computer freezing up or slowing down?
Repair corrupt files and harmful errors - protect your PC
Take a 2-minute PC health check-up at no charge!
http://click.topica.com/caaedmqbz8Qcsbz9JC9a/PC PowerScan
-------------------------------------------------------------------
Jim,
If you put the Sunny Island between the two panels you will solve your
problem. Connect the AC input of the SI to a breaker in the main panel
and connect the output to the sub panel. AC will flow through the SI
when utility is present and the SI will power the sub panel when there
is no utility power (and separate the panels). The output of the
Sunnyboy inverter should be connected to a breaker in the sub panel so
it will continue to work when utility power is off.
This can also be accomplished with a Xantrex SW or an Outback inverter,
but the Sunny Island does an elegant job of talking to the Sunnyboy when
solar output is greater than load usage during a power outage. All of
the inverters will charge the batteries if the sun is out, the utility
is down and usage in the house is lower than array output.
Good luck.
David
David Katz
President, AEE Solar
formerly Alternative Energy Engineering
1155 Redway Drive - Box 339
Redway, CA 95560 USA
Phone (707) 825-1200
Fax (707) 825-1202
email: david at aeesolar.com
web: www.aeesolar.com
Jim Duncan wrote:
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Is your computer freezing up or slowing down?
>Repair corrupt files and harmful errors - protect your PC
>Take a 2-minute PC health check-up at no charge!
>http://click.topica.com/caaedmqbz8QcsciHNopa/PC PowerScan
>-------------------------------------------------------------------
>
>Wrenches,
>I have started a grid-tied PV installation with backup batteries for a
>rural residence. Now the owner wants to include a critical load
>sub-panel next to the main service panel. :>O
>The equipment room, containing batteries, 2 SMA 3800s and 2 Sunny
>Islands is 160 feet from the house and the ground in between is rock. I
>really don’t want to send the rock saw back through the landscaping and
>yard to get power to the sub-panel.
>To power the sub panel off the main service is the goal but I need to
>find a way to lock out the rest of the non-critical loads while still
>feeding off that main service panel. The mains lock out must happen the
>same instant the Islands detect the utility loss and kick over to
>battery power.
>I know this must have been done before by lots of other installers but
>this will be a first for me. Can this be done without running any
>conductors, LV relay wires, or wireless signal, between the buildings?
>Thanks in advance.
>
>Jim Duncan
>North Texas Renewable Energy Inc
>817.917.0527
>ntrei at earthlink.net
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>FREE DVR
>And up to 3 additional standard receivers!
>Call 1-800- 901 - 5080 Today
>http://click.topica.com/caaeas1bz8QcsciHNopf/DirectSatTV
>-------------------------------------------------------------------
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
>
>
>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
FREE DVR
And up to 3 additional standard receivers!
Call 1-800- 901 - 5080 Today
http://click.topica.com/caaeas1bz8Qcsbz9JC9f/DirectSatTV
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list