Bob-O,

Safe opening of the fuse holder assumes the polarity is correct on the
source circuits and no ground faults. ;-)

An important safety procedure is to always check the circuit current on the
strings feeding the fuses. If there is reverse polarity or a ground fault,
significant current could be flowing that would burn down the fuse block if
opened under load. With either of these problems, urrents can flow even with
the disconnect open.

If current is flowing, wait until sundown to open the fuses. If you're
impatient, the whole array must be covered with an opaque material (that's
loads of fun).

Bill.

-----Original Message-----
From: Bob-O Schultze, Electron Connection [mailto:econnect at snowcrest.net] 
Sent: Monday, August 01, 2005 1:22 PM
To: RE-wrenches at topica.com
Subject: Re: Series fusing for string installations [RE-wrenches]

Marco, William and all,
Another option would be to use a small rack mounted fused combiner box 
like Energy Outfitters sells in conjunction with a regular H361 at the 
inverter or an inverter such as the Fronius or Xantrex which has the DC 
disco onboard. That way you've got just one set of conductors coming 
down from the roof. Once the big switch is open, the HV touch-safe fuse 
holders can be opened safely.
Bob-O
>
> Why not use the nifty Combi-Switch which has four Littelfuse high
> voltage
> fuse holders integrated into a CTL listed HU361RB disco and enclosure?
>
> marco
>


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list