Just a quick note:
THe MX-60 will still be sending a Pulsed signal back down the line to the
array as it modulates the array current. I've heard C-40 modulation at the
solar panels 200 ft away. ALso while not recommended, I've run Trimetric
meter wire in conduit with AC wires without a problem, the twisted pairs
cancelled any noise.
Ray
>Thanks John, Jeff, Dan and Jay,
> Yes, to what degree that this may be a problem sounds like is still
> somewhat of a mystery and probably won't be a problem from what you all
> have shared. Unfortunately the customer's mind will most likely not be at
> ease unless I can prove that it surely won't be a problem for him. The
> MX-60 is at the end of the line so hopefully there won't be any PWM noise
> on the AC line. If the wire is re-pulled at least the twisted Tri-Metric
> wire and Mate cable can be placed in the conduit alongside the DC solar
> wires where the undersized #6 AC wires are now. Luckily they did wire the
> battery/inverter cables alone although they only hooked up one set and
> stole/took the other set home to hide so the customer would not know they
> were left over -similar to the Tri-Metric and GFP/2 that was pushed aside
> in the "parts left over" area.
>
> I would still like to hear more on the fundamental electrical
> engineering issues as Jeff stated if anyone has anything to add. Thanks
> again for all the responses,
>
>Nick A Lucchese
>
>
>
> From an electrical engineering standpoint, well... it all depends.
>>The one thing that you NEVER want to do, if at all possible, is to run
>>high impedance DC SENSE or metering lines in the same conduit as 120VAC,
>>definitely not without properly terminated shielding.
>>
>>In the case of DC power lines running along side of AC power lines, the
>>impedances of both the AC and DC lines tend to be low in comparison to
>>sense circuits, so a given amount of interference energy will not induce
>>anywhere near the amount of actual voltage on the other line, as it would
>>in a high impedance metering circuit.
>>
>>That doesn't mean that you're home free, though. A "DC" solar
>>array/charge circuit still probably uses high frequency PWM circuits to
>>regulate charge, and those pulsing currents can induce small potentials
>>on the AC lines. Shouldn't be a problem unless it interferes with the
>>sense circuits on the output of the inverter, or on the input circuits of
>>an intelligent appliance. I've never heard any such cases, but I could
>>see where pulsed PWM noise from a charge controller could interfere (in
>>theory) with the sense circuitry associated with an inverter's search
>>function, or with other inverter output metering circuits. The inverter
>>manus would have to comment further as if there's any real possibility of that.
>>
>>Running battery/inverter cables in the same conduit as AC lines could be
>>a real mess. There's a lot of high-energy current pulsing occurring on
>>the DC lines when the inverter is powering loads, much higher than a
>>typical solar charge circuit. I wouldn't want that combination to occur
>>in any circumstance, not that I could imagine that ever happening.
>>
>>
>>Conversely, AC noise, coupled onto the DC lines, could mess with the
>>sense circuits on a charge controller, but I would expect that those
>>sense circuits would be pretty heavily filtered in all but the lowest end
>>products, since there's no reason not to.
>>
>>Just my $0.02 for what it's worth,
>>
>>John Raynes
>>RE Solar
>>Torrey, UT
>>
>>
>>At 08:56 AM 6/21/2005 -0700, you wrote:
>>>Hey Nick and Jay and all,
>>>
>>>Yes there is a provision in the code "if part of the same system" but
>>>beware. Not only can you run into interpretation issues by inspectors
>>>there is a very real possibility of induced currents and noise. I'm not
>>>an expert on it but from my experience with high voltages and amperages
>>>in electric vehicles, DC current can cause some serious induction
>>>currents. So you may get away with it on a code level but the physics
>>>of the matter should really be checked out! At the amperages you are
>>>talking about with your PV system - they may not be a problem - but it
>>>would be nice to quantify that.
>>>
>>>Anyone out there with a fundamental electrical engineering head better
>>>than mine know the really issues, here?
>>>
>>>Best,
>>>
>>>Jeff C.
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Erase wrinkles without painful injections with Nexiderm SP.
Nexiderm SP is clinically proven to reduce wrinkles by 68% Click
here to get your 30-day free supply.
http://click.topica.com/caadAclbz8Qcsbz9JC9f/Nexiderm
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list