Allan,
Presumably there will be signs of current having passed from your steel
junction box and the mounting pole as well because of the galvanized
pole exterior and the painted mild steel of the box and what happens
when the surfaces are wet. What sounds kind of weird is the amount of
damage to the pole. Was this all new material when installed?
Aside from the questionable installation job, I doubt that Ron and Mike
would suggest using a 5" pole in lieu of 6", especially if the area is
subject to the occasional 60 MPH gust, but maybe you could fill the pole
with concrete to stiffen it up. I have successfully used this method on
a gas tracker after discovering that the owner/installer of the pole had
somehow misconstrued ID and OD dimensions. (Where he found 5.5" pipe is
a mystery). I had an adapter fabricated to fit the tracker socket and
used 4 set screws to keep things solid. It's been through 90 MPH plus
storms with no problem (so far!) You can't "repair" a rusted-through
pole since there is nothing solid enough to weld if it's gone at ground
level.
Using diagonal braces and collars sounds pretty ugly.
It's too bad that your installer wasn't aware of plastic strain reliefs
when he did the job; they've been around since well before '97, as have
the aluminum variety. It's also too bad that he ran his ground wire
along with the PV wires. :-( I admit to having used Romex clamps for
years (starting in '80) in outdoor installations, up until the right
stuff became available, and never had anything remotely like this happen
(fortunately) But then my ground wires only grounded the array and pole
because I mostly used Carlon boxes! :-)
Good luck,
Matt T
Allan Sindelar wrote:
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Sign up today for a No Annual Fee Discover® Platinum Card and get…
>0% Intro APR on Purchases & Balance Transfers for 8 Months, Up to
>2% Cashback Bonus® reward on your purchases & 100% fraud
>protection.
>http://click.topica.com/caadtrVbz8QcsbadqCja/DiscoverCard
>-------------------------------------------------------------------
>
>Wrenches,
>A simple mistake can have major consequences.
>
>In 1997, in my first year of business, I designed and sold a SW4024-based
>grid-tied system for a new home. As I wasn't licensed at the time, another
>local electrical contractor with a history of doing solar installations was
>separately contracted to pull the permit and do the installation. Upon
>completion, I corrected a few things I didn't like (battery cables connected
>at one end of the bank, rather than diagonally, for example) and have
>supported the system and the customer in the years since. This is a good
>customer.
>
>The system has worked well, with only the Wattsun tracker and the E-Meter
>requiring repair or replacement. The client called recently about tracker
>malfunction, and today Mark (partner) went to the site to service it. What
>he found was battery voltage at the tracker ground, which he determined was
>from a ground fault at the array. The galvanic action caused by the fault
>had rusted the 8-year-old 6" Sch 40 steel pole to the point that he could
>poke a screwdriver through the pole at the base, and was concerned about the
>whole thing toppling over any minute.
>
>The cause of the ground fault was the use of two 1/2" Romex clamps for
>strain relief where the USE-2 array input conductors entered a steel 3R
>combiner box on the pole. Each of the two clamps held four #10 USE-2
>conductors and one bare #8 or #10 grounding electrode conductor. One of the
>clamps had shorted one of the PV+ conductors to ground. I am guessing that
>it had been like this for a long time, maybe since installation, and I had
>never detected the fault during routine service calls. An array GFDI wasn't
>installed or required (and I'm not sure anyone even made one at that time).
>
>The customer is looking at repair options for the pole, including outriggers
>with driven steel posts and welded braces, and a poured concrete cap over
>the base of the pole. We will head out soon to disassemble the array, to
>reduce wind sail and the chance that it will come down, and to buy some time
> for a good repair to be devised. We are also looking at setting a 5" steel
>pole inside the 6", with cement slurry between the two.
>
>We haven't worked out a course of action yet. A couple of questions:
>
>We use SO connectors for USE wire, and use Romex clamps for jacketed wire in
>indoor locations. Is the use of Romex clamps on USE wire in this application
>legal per NEC? What Code section addresses this?
>If issues of liability and responsibility come up (and they probably will
>not) who's liable? The contractor who installed the system and pulled the
>permit? The inspector who signed off on the job? Us? How would you serve the
>customer in this case? I supplied a one-year warranty on system design and
>component failures, and the installer gave the same against failures due to
>incorrect installation.
>
>Has anyone ever repaired a rusted pole? Howdja doit, and did it work?
>
>Thanks for any good advice. I'll share your responses with the client.
>
>Allan at Positive Energy
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Need a Laptop? Get a Sony Vaio Laptop Free!
>http://click.topica.com/caadtaFbz8QcsbadqCjf/ProductTestPanel
>-------------------------------------------------------------------
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
>
>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Sign up today for a No Annual Fee Discover® Platinum Card and get…
0% Intro APR on Purchases & Balance Transfers for 8 Months, Up to
2% Cashback Bonus® reward on your purchases & 100% fraud
protection.
http://click.topica.com/caadtrVbz8Qcsbz9JC9f/DiscoverCard
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list