Thank you Allan
I think you have it about nailed. My customer wanted
a second opinion, and I thank you for the logic behind
your method.
Darryl
--- Allan Sindelar <allan at positiveenergysolar.com>
wrote:
> Darryl,
> Starting with a better quality unit, that can be
> counted on to deliver continuous output, figure
> inverter maximum (or desired) AC input, divided by
> (deration for elevation above sea level times
> deration for how close to maximum rated output we
> want to run it).
>
> For elevation deration we use mfgr's specs, or 3.5%
> per 1,000 ft above sea level if no mfgr's specs.
>
> Example: An Outback VFX can take a maximum of 19A AC
> in, I believe. At 6,000 feet that's 3.5 X 6 = 21%;
> 100 - 21 = 795, or 0.79. If I want to run the gennie
> at no more than 85% of maximum output, then:
>
> ____19___
> 0.79 X 0.85 = 28.3A @ 120V, or at least 3,400
> rated watts.
>
> Then adjust for other factors, like 120V output
> availability; if 120/240 only you need a step-down
> transformer, with its attendant losses; reputation
> of the generator for hangin' in there when you work
> it that hard; wire losses, if distance is involved,
> and power factor. Inverter efficiency doesn't play
> directly into this equation, as it more affects DC
> output.
>
> On a big off-grid system we are doing, two VFX3648s,
> using "Outback stacking" with the Hub, is plenty to
> run the house and barn. However, we are using a Quad
> Stack in order to get the charging C/ rate up high
> enough; the other two inverters are just for
> charging. At 6,500 feet, we need 18kW including
> derations, and are using an Onan RS20000 unit.
>
> Hope this helps.
> Allan @+E
>
> ----- Original Message -----
> From: "Darryl Thayer" <daryl_solar at yahoo.com>
>
> > What logic process do you use to size a generator?
> If
> > the generator is oversized and runs at part load
> its
> > effiecency is affected, also my customer is afarid
> of
> > diesels in cold minnesota climate and would perfer
> a
> > propane generator.
>
> [Non-text portions of this message have been
> removed]
>
> Your free subscription is supported by today's
> sponsor:
>
-------------------------------------------------------------------
> Make phone calls with phone service from
> Packet8.Order VoIP
> today & get Free Activation, Free Equipment & First
> Month
> Free! Packet8 30-day money back guarantee.
> 1-877-868-1135
> http://click.topica.com/caaegt4bz8Qcsbd5Ekwf/ TMONE
>
-------------------------------------------------------------------
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios:
> www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
More information about the RE-Wrenches
mailing list