Hey Ray,
I'm glad you appreciate the PV System Design Worksheet that I shared
with the Wrenches a couple years ago.
You're probably right about the redundancy that you describe. Then
again, how do you determine the inverter efficiency? It's really low
during low-load hours, but that bears less weight in the energy calc.
Your 92% may be high for a modest remote home, for that reason. I
believe that the best we can do is refine our guesswork, be
conservative, and accept the nature of the game.
I entered a default battery efficiency of 88% thinking it is already
high, to account for relatively high daytime loads with no loss. If all
loads were at night, efficiency would be 80-85% with good batteries and
a well-designed charging scheme. Even then, there are different ways to
define and determine batt efficiency.
Doug's advice about customers always using more than they calculated
points to always calc'ing on the high side anyway. I know you agree.
I won't comment about your off-grid biz woes, but to say that I hope
the PV dealers who are drawn to strictly grid-tie will leave more and
better off-grid biz to guys like you who really light the field.
Windy
> Date: Wed, 27 Jul 2005 22:21:26 -0600
> From: Solar Ray <ray at solarray.com>
> Subject: Inverter Load Analysis
>
>
>
> Hi All;
>
> I have possibly a dumb question: I use a spreadsheet originally
> designed by
> Windy Dankoff, and it figures inverter average efficiency into the
> total
> energy calculation. I added a page that lists all the appliances and I
> list
> the inverter no load draw times the hours it will be on. Is this
> redundant?
> I use a 92% efficiency number for the inverter overall, but should I
> raise
> this, since I'm adding in the inverter's no load draw in the other
> page?
> For an average load of say 500 watts and a no load draw of 10 watts,
> that
> is about 2% of the total inverter draw. I'm considering raising my
> inverter
> efficiency number by 2% to account for this.
> Also, I was considering raising my battery efficiency number
> (currently I
> figure 88%) because many of the big loads (refrigeration, water
> pumping)
> occur more in the day, and so the battery isn't be cycled as much to
> power
> those loads. I was considering going up to 90 or92% for average battery
> energy efficiency on projects with larger daytime loads. (notice I said
> "energy efficiency" which is charging efficiency x voltaic efficiency)
> Off grid design seems to be much more difficult and time consuming than
> grid tie stuff. A lot more call backs too. I wonder if the days are
> numbered for us old fashioned off grid load analysis freaks. 10 times
> the
> trouble for half the pay will send even the best of us looking for
> rebate
> programs.
>
> Ray Walters
> ray at solarray.com
> President, SolarRay, Inc.
> NABCEP Certified Solar PV Installer
> BS Mechanical Engineering, UT Austin 88
> Returned US Peace Corps Volunteer
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Erase wrinkles without Botox! Nexiderm SP is clinically proven to
reduce wrinkles by 68% Click here to get your 30-day free supply.
http://click.topica.com/caadHllbz8Qcsbz9JC9f/Nexiderm
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list