DCBB (was SW4024 with control problems) [RE-wrenches]

Allan Sindelar allan at positiveenergysolar.com
Wed Jul 6 14:40:06 EDT 2005


Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get $1000.00 Overnight! Fast and Easy!
No Credit Checks! Many Lenders are 100% Paperless!
Let The Wizard Find the right Lender for you!
http://click.topica.com/caadHk8bz8Qcsbz9JC9a/911PaydayAdvance
-------------------------------------------------------------------

We have learned from experience to put anti-sieze on all of the set screws
in the DC bonding block. Otherwise, the set screws will often not tighten
sufficiently when new, due to friction. This may have caused the initial
overheating Matt saw. Over time, heat/cool cycling causes more loosening,
which causes more heating, ad nauseum. Also, without anti-sieze or a similar
thread lubricant, they can corrode in a few years to the point that they can
freeze in place.
Allan at Positive Energy

----- Original Message ----- 
From: "Matt Tritt" <solarone at charter.net>
I think I've traced all the problems back to a 4/0 cable
connection (-) that managed to loosen-up over about 4 years. It wasn't
so difficult to find the problem, seeing as how the DC bonding block got
hot enough to fry some of the insulation off a controller lead connected
to the same block. I am not a big fan of the
bonding block arrangement in the Trace DC box for several reasons, not
the least of which is it's deep location - way to one side, which can be
a hassle in some installations.

So, even if your problem is not the negative connection, I suggest
re-torquing all the connections within the DC enclosure to original
spec's as a preventative measure. But you probably already did that!

Matt

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Erase wrinkles without painful injections with Nexiderm SP.
Nexiderm SP is clinically proven to reduce wrinkles by 68% Click 
here to get your 30-day free supply.
http://click.topica.com/caadHlnbz8Qcsbz9JC9f/Nexiderm
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list