Jeff O. and Jeff C.,
OutBack can only do three inverters in a three-phase application. One
inverter (3.6kW max) per phase. They haven't worked out the communications
for stacking multiple inverters on each phase yet.
Take a look at the Exelteck MX series. They can do up to 60kW at 208V
three-phase with up to a 120VDC battery bank. Excelent inverters, although
not super efficient. Figure on 10W idle loss per 1kW MX Power Module and 85%
conversion efficiency. Exeltech could also probably make them with a higher
voltage input
You should also look into the SMA Sunny Island system, especially if these
apps are overseas. The US version is not ready for three-phase (yet), but
the European model is.
Cheers,
Brian Teitelbaum
AEE Solar
-----Original Message-----
From: Jeff Oldham [mailto:starpower4u at juno.com]
Sent: Monday, June 20, 2005 4:48 PM
To: RE-wrenches at topica.com
Subject: Help w/large o-t-g inverter! [RE-wrenches]
I'm having a heck of a time (again!) trying to find a 30-40 kW o-t-g battery
based inverter. I need 3 phase perferably 240 or 208 VAC as I don't want to
feed transformer cores. I think wire is cheaper and more reliable than
transformers and more PV to cover tare loses. Even though my
transmission/distribution issues are not slight, I'm still leaning in this
direction.
I would love a battery over 200 VDC but will take anything. I've used the
options from Australia and care not to repeat the experience. I have 2
applications both outside the U.S. so U.L. is not going to limit my choices.
Genset interface and a battery charger will make life easier too (since I'm
askin')!
Any ideas??
Thanks,
-jeff o
>From the Solar, Wind and Hydro powered office of Jeff Oldham
Moderator: michael.welch at homepower.com
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get $1,000 to spend on groceries⦠any way you please. Click here!
http://click.topica.com/caadAcAbz8Qcsbz9JC9f/GrocerySpree
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list