Sharp modules - now 150 vdc approvals [RE-wrenches]

Christopher Freitas --- OutBack Power cfreitas at outbackpower.com
Thu Mar 3 13:30:16 EST 2005


Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Want a laptop? Get an Apple iBook for free! 
http://click.topica.com/caadeMmbz8Qcsbz9JC9a/Amazing Computer 
-------------------------------------------------------------------

Wrenches - 

Yes we did complete the relisting of the MX60 MPPT charge controller to 
150 vdc max along with all of the breakers (up to 80 amps DC).    This 
voltage of course is the maximum open circuit voltage produced by the PV 
array under the coldest conditions for the paticular site.  

This will allow use of the MX60 with 3 in series 24 vdc PV modules type 
arrays in more locations - but still not all locations.  It also varies 
with the particular module used.  

The new max voltage rating for the breakers is an additional ETL 
approval on the breakers specifically for use with PV arrays only.  This 
was the fastest solution we could come up with as the breaker 
manufacturers are pretty slow to make changes and still view the PV 
market a speck of dust compared to their other markets.  Hopefully we 
will get one of them to add the listing to the standard breakers.  

This higher voltahge rating applies to all of the OBDC and OBPV breakers 
as well as the OB-GFP/2 ground fault protection device.

The copy of the authorization letter should be on our website within a 
few days for you to use if questioned by an inspector.  

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com  
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030  

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get a FREE* MP3 Player - yours to keep! Click Here Now!
http://click.topica.com/caadeMpbz8Qcsbz9JC9f/MP3 Player Giveaway
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list