Christopher,

Question about overcurrent protection. If you push beyond 120Vdc, will your
documentation provide alternatives for fusing since the breakers are
unlikely to reach that rating. BTW, I noticed that Bussman's 170Vdc fuse has
been UL listed and has made it into some Home Depots. I saw them in Hawaii.

Bill.


-----Original Message-----
From: Christopher Freitas --- OutBack Power
[mailto:cfreitas at outbackpower.com]
Sent: Tuesday, September 21, 2004 12:36 PM
To: RE-wrenches at topica.com
Cc: rgudgel at outbackpower.com
Subject: RE: MX60 question [RE-wrenches]

marco mangelsdorf wrote:
> The BP3160Q is an oddball module with a 23.8 Vmp and 30 Voc.  So four in
> series here in the tropics shouldn't come close to the 140V max for the
> MX60, right

Sorry for the slow response on your question - glad to see others
helping out.  I actually was visiting Darryl Thayer's 40kW+ OutBack
gridtie system on Friday - very impressive installation that is working
well - although he had to do too much custom installation hardware as
the space allowed for the equipment was very small and challenging.

If the VOC on the modules you are using is 30 VDC and the location
doesn't get too cold (below freezing) than I would say your fine.  It is
likely that the open circuit voltage will exceed our current ETL listing
of 120VDC - we are planning on retesting soon to increase the approved
limit to the factory max VOC rating of 140VDC.

As far as the choice of going with a one, two, three or four in series -
it depends on numerous factors such as the distance of the PV array to
the controller and if any partial shading is present. From my
observations so far - I think wiring panels up for high voltages when
short distances are involved compared to putting them in parallel is a
wash - yes the efficiency of the MX60 goes down slightly with the high
PV array voltages charging into a low battery voltage (about 1 or 2
percent less) but the losses in the wiring are less and the PV array
will start charging slightly earlier and will work better under
partially shaded conditions and when subjected to high ambient
temperatures.

We have recently installed two identical PV arrays which will allow us
run side-by-side tests of both a low voltage system and high voltage
system charging into the same battery with the voltage being sold back
into the grid.  The results of this will be published on our website and
I will announce it once available.

As far as moving to Hawaii - keep in mind that there is areas with snow
there too!

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Click here and walk away with your free Chevy collectible.
http://click.topica.com/caacDvMbz8QcsbaaVcJf/PermissionData
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Save up to 67% on Omaha Steaks + Get 6 FREE Burgers and a 
FREE Cutlery Set + Cutting Board!
http://click.topica.com/caacBBEbz8Qcsbz9JC9f/OmahaSteaks
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------







More information about the RE-Wrenches mailing list