4/0 represents a lot of copper
I'm with Ray here...
I'd venture that the internal resistance L16 batteries and terminals
waaaaaay overshadows the trivial drop from a few feet of 2/0 cable.
The SW does seem to take many milliseconds to catch up after
a jump in demand or a transfer from utility interactive to isolated;
while it catches up, the AC voltage does seem to sag noticeably.
/wk
Hi Matt;
>The manual says 2/0 to 5 ft, 4/0 to 10 ft. I'm cheating by a foot or
>two. The 175 A at 24 VDC draw is 0.1 second peak from the circular saw; it
>is not anything close to continuous run amps. Battery bank is 8 L-16s. DC
>voltage at rest is 24.6v, surge drops the voltage to 23.2. Again, that is
>a 0.1 sec minimum. I have always noticed batteries pull down like that for
>a second on start up surges.
>I'm going to change the cable to 4/0, but I don't think that is going to
>fix it. I have a few of these SW + inverters installed with similar
>complaints of lights flickering, etc when an inductive load comes on. They
>all have 4/0 cable BTW.
>
>Ray
>
>> Hmmmmmm.
>>
>> You say that you're running a 2548 on 2/0 inverter cables. First-off, my
>>recollection about the SW 12 and 24 volt versions is that they actually
>>require 4/0 cables to begin with becuase of the possibility of a 400 amp
>>surge under certain startup conditions.
>>
>> It also sounds like the batteries are on the low side, which also doesn't
>>help much, but 175 amps draw? I hope this is on your Skillsaw and not the
>>Staber. ;-)
>>
>> How long are your inverter leads and how big is the battery bank?
>>
>> What is the problem with the Washer?
>>
>> Matt T
>> ----- Original Message -----
>> From: "Ray Walters" <ray at solarray.com>
>> To: <RE-wrenches at topica.com>
>> Sent: Friday, August 13, 2004 10:46 AM
>> Subject: SW+ Voltage Sag [RE-wrenches]
>>
>>
>>
>>
>> Your free subscription is supported by today's sponsor:
>> -------------------------------------------------------------------
>> Need cash fast? Get a $500 CASH ADVANCE overnight! Let
>> YourCashCentral get you the cash you need.
>> http://click.topica.com/caacxycbz8QcsbadqCja/MyOnlinePayday
>> -------------------------------------------------------------------
>>
>>
>> >Dear esteemed colleagues;
>>
>> I am currently troubleshooting a Staber Washer control malfunction on an
>> Xantrex SW2524+ inverter. What I found curious is that the voltage sags
>> down to 88 VAC rms for about a tenth of a second during starting surge. I
>> am using a worm drive circular saw after to test. Measurements are at the
>> inverter AC terminals with a Fluke 89 set to normal MIN capture.(the fast
>> capture would get the bottom of the wave form itself) I also measured the
>> DC side and found the voltage to be 24.6 vdc at rest with the surge
>>pulling
>> it down to 22.9 vdc (again regular MIN capture on the Fluke). MIN volts
>>for
>> 0.1 secs at the battery terminals was 23.2 vdc. The DC current surge
>> measured at the shunt block with the Fluke was an amazing 175 amps for 0.1
>> secs. AC current was harder to measure surge, but I saw a 27 amp peak at
>> the Inverter's onboard meter.
>> My question is this: Is it normal to see a temporary voltage sag like this
>> when powering a heavy inductive load. I rechecked all my connections AC
>>and
>> DC. I looked for volt drop at any tell tale points, etc. I am thinking its
>> an inductive issue with the DC cables, and so my next visit I wanted to
>> upsize the cables to 4/0 and twist the cables around each other.
>>Everything
>> else on the system seems to work great, other than occasionally a UPS box
>> for the computer beeps, again with a start surge from another appliance.
>> Your feedback, wisdom, comments, & of course criticisms are all greatly
>> appreciated.
>>
>>
>> Ray Walters
>> ray at solarray.com
>> President, SolarRay, Inc.
>> NABCEP Certified Solar PV Installer
>> BS Mechanical Engineering, UT Austin 88
>> Returned US Peace Corps Volunteer
>>
>> Your free subscription is supported by today's sponsor:
>> -------------------------------------------------------------------
>> Get a Great Credit Card for You Today
>> You can find a credit card to fit your credit needs.
>> All types of credit cards -- 0% APRs, Rewards, & Bad Credit.
>> http://click.topica.com/caacvgubz8QcsbadqCjf/411Web
>> -------------------------------------------------------------------
>>
>> - - - -
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages:
>>http://lists.topica.com/lists/RE-wrenches/read
>>
>> List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Hosted by Home Power magazine
>>
>> Moderator: michael.welch at homepower.com
>>
>>Your free subscription is supported by today's sponsor:
>>-------------------------------------------------------------------
>>RE-GROW YOUR HAIR STARTING NOW.....Click here for more info!
>>http://click.topica.com/caacxydbz8QcsbeuiVOf/Medical Hair Restoration
>>-------------------------------------------------------------------
>>
>>- - - -
>>To send a message: RE-wrenches at topica.com
>>
>>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>>
>>List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
>>
>>Check out participant bios: www.mrsharkey.com/wrenches/
>>
>>Hosted by Home Power magazine
>>
>>Moderator: michael.welch at homepower.com
>
>Ray Walters
>ray at solarray.com
>President, SolarRay, Inc.
>NABCEP Certified Solar PV Installer
>BS Mechanical Engineering, UT Austin 88
>Returned US Peace Corps Volunteer
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Shop online for Discount Auto Parts: Mirrors Headlights Tail Lights
>Bumpers Fenders Window Regulators Spoilers Altezza Lights and a Full Line
>of Auto Body Parts. www.partstrain.com
>http://click.topica.com/caacxygbz8Qcsbdh77Hf/Parts Train
>-------------------------------------------------------------------
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
>
>
>
>---
>Incoming mail is certified Virus Free.
>Checked by AVG anti-virus system (http://www.grisoft.com).
>Version: 6.0.737 / Virus Database: 491 - Release Date: 8/11/2004
--
[Non-text portions of this message have been removed]
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get a Great Credit Card for You Today
You can find a credit card to fit your credit needs.
All types of credit cards -- 0% APRs, Rewards, & Bad Credit.
http://click.topica.com/caacvgubz8Qcsbz9JC9f/411Web
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list