Allan,
Rather than making the main service panel be 300A, we prefer to make a
main tap, then run to a fused AC disconnect with fuses rated at 50% of
the inverter sub panel buss, and the buss rated at 200% of the inverter
breakers. This meets NEC690.64, and is not too big a hassle.
Can't wait for 2005 code...
Jeff Wolfe
-----Original Message-----
From: Allan Sindelar [mailto:allan at positiveenergysolar.com]
Sent: Thursday, April 01, 2004 1:20 PM
To: RE-wrenches at topica.com
Subject: Re: Multiple Sunnyboys [RE-wrenches]
Kirk,
This is an appropriate method. We did this with 2 1800s and 2 1100s
recently, and it took 6 breaker spaces--you'd The smallest box that
could do this is a QO8-16/100RB, though I might pick a bigger box just
to have more warehouse space for wiring. However, a couple of notes of
caution:
1. You must size the conductors between the AC combiner box/breaker
panel for 60A @ 240 VAC with ~1% voltage drop. Size your conduit
accordingly.
2. At 15A X 4 = 60A AC, your main residential service panel must be at
least 300A.
Hope this helps.
Allan at Pos E
----- Original Message -----
From: "Kirk Herander" <kirk at vtsolar.com>
I am installing a 10KWP system using 4 Sunnyboy 2500 watt inverters. On
the AC side, it would be most convenient to backfeed a subpanel with the
4 outputs, then have a single 240 circuit between the sub and main
panel, roughly 100' away. It beats running 4 seperate circuits directly
to the main, and I can also monitor total array output with a single KWH
meter this way. Any pitfalls to this method?
===========================================================
MORTGAGE / REFINANCE RATES ARE LOW. ACT NOW!
3 Mortgage brokers compete for your business.
Great rates, no obligation, and easy form.
http://click.topica.com/caab6aabz8QcsbAltH2f/ Insurance4usa.com
===========================================================
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
===========================================================
**** Bounces like rubber! Shatters like ceramic! ****
Discover Crazy Aaron's Thinking Putty in grown up
handfuls. It's the creativity unleashing, mood enhancing
desk toy!
http://click.topica.com/caab593bz8Qcsbz9JC9f/ Crazy Aaron Enterprises
===========================================================
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list