Allan,
I think the best argument is that no one else is doing it. In Wisconsin,
we wrestled with this issue in a collaborative with the utilities and
regulators. Luckily our voices prevailed after conveying the magnitude of
the burden a PE stamp would impose on the sale and installation of
non-commercial systems.
Wisconsin simply requires that the installer/designer be identified on the
interconnection application. That way, the utility can contact him/her if
questions come up. If you, or anyone else wants, I can send the
"Interconnection Application" form developed for residential systems --
defined here as 20kW and less to match our net-metering laws.
Keep in mind though, the utility should have NO jurisdiction over the
"design" of the system. Concerns about safe design should be left to the
homeowner, designer, installer and local inspectors. The utility's
jurisdiction should stop at the point of common coupling -- the
interconnection point. Moreover, their review of the application should be
limited to review of:
1. Certification to, or functional compliance with UL/IEEE standards
2. Adequate system protection with respect to fault currents
3. Minimum power factors to ensure stability.
Its fair and reasonable for the utility to ensure the safety and
performance of their systems won't be affected by our installations and we
should provide the information and data necessary for them to make that
determination. However, any effort by the utility to extend its reach
further than the point of common coupling must be vigorously opposed. The
don't let us have say in the design of their systems -- they shouldn't have
any say in our designs!
Good luck,
David
At 05:20 PM 3/10/2004, you wrote:
>Fellow Wrenches.
>New Mexico has net metering and a newly-codified RPS. We have worked with
>four utilities (one IOU and 3 RECs), all of which are regulated. Now we are
>working with a client (and there may be more coming) in the city of Los
>Alamos, which is a muni and thus unregulated by our state's PRC. The client
>is having us install 3 kW of PV on a Wattsun Uber-tracker in his back yard,
>as he rebuilds after the 2000 fire.
>
>The Los Alamos County Utilities Dept. is drafting a net metering agreement
>as we speak. The issue I want to protest is a requirement that "the
>qualifying facility to be designed by an engineer licensed in NM." Nobody
>else requires this, and it would add several hundred bucks to the system
>cost.
>
>Can anyone provide a well-written argument against requiring an engineer's
>stamp, from another battle elsewhere that I may use to craft a comment on
>the proposed rule? A word document would be great, as I can cut and paste it
>onto letterhead and submit it to the utility.
>
>Thank you for any help.
>
>Allan at PosE
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
----------------------------------------------------------
David Blecker, PE, Executive Director
Seventh Generation Energy Systems, Inc.
608-424-1870 (ph) 424-1810 (fax)
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list