They have a 10,000A DC plant and rivers of 750 MCM cable running about the place.

Timeframe is probably 2-3 months but I can check to make sure.  It could easily be setup as several smaller banks, maybe one per 19" or 23" bay.  What kind of power (complete system with DC & AC disconnects, etc.) could you get into a 7' bay?






--On Wednesday, February 25, 2004 2:54 AM +0000 Christopher Freitas --- OutBack Power <cfreitas at outbackpower.com> wrote:

> The current draw of the inverter will be over 4000 amps at 48 vdc for a
> 180 kWAC inverter system - impressive.  I know it is actually done in
> the telcom world - just thought the current levels involved sounded
> wild.
>
> Technically, it is possible for us to do this with the OutBack FX series
> - and we do plan on doing it - we just need to make a master control
> unit out of an inverter control board and a AC board - we already have
> the redundancy working in the present product (except that we use one FX
> inverter as a master - all the slaves inverters can already be "hot
> swapped" or shutdown without any issues.  With a master control unit all
> the inverters will operate as just slaves.
>
> What is your the time frame required for the delivery?
>
> You might talk with RMS electric in Boulder, Co - Mark or Jan - I know
> they have sold some large telcom inverters in the past that were similar
> (www.rmse.com).
>
> Christopher
>
>
> Kurt Albershardt wrote:
>>
>> I have a client looking for 150-180 kVA of 120-240V from their
>> (existing) -48V telecom power plant.  The Exeltech GX stuff is still not
>> ready and I'm wondering what other options might be suitable to the task
>> (low distortion, N+1 redundancy, alarming & monitoring via SNMP or
>> similar.)
>>
>>
>> --thanks
>
>
>
> Christopher Freitas
> OutBack Power Systems, Inc.
> cfreitas @ outbackpower.com
> www.outbackpower.com
> Arlington WA USA
> Tel 360 435 6030
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------






</x-flowed>


More information about the RE-Wrenches mailing list