mm 5000 [RE-wrenches]

Rosenfeldt, Marko rosenfeldt at beaconpower.com
Tue Feb 24 15:00:09 EST 2004


Hello Max,
First I would like to address the technical issue you raised.  The scenario you are seeing with the Advanced Energy MM5000 is a fault that causes the inverter portion of the system to turn off.  When this happens, early software versions of the MM5000 did not switch the utility to load or grid-to-load.  The system does come with a built-in bypass function that works in the following manner:

Turn OFF all input breakers:
	Grid
	Inverter / Load
	PV / DC Disconnect
	External Battery Disconnect

Then turn ON only the Grid breaker.

The unit will then be in bypass mode, with critical loads powered by the utility until the MM5000 can be checked out for further action.

If you’d like more Advanced Energy documentation and support docs, you may find them in the Support section of the Beacon Power web page:

http://www.beaconpower.com/support/AdvancedEnergyProducts.htm

As far as your call to our office is concerned, Beacon Power is dedicated to professional customer service, and our intention is that phone calls be returned in a timely fashion.  I apologize if this did not happen in your case.

For installers / owners of AEI MM5000 / MM3000, Beacon is offering a $1000 trade-in rebate.  The rebate will be applied after the purchase of a new Smart Power M5, which comes with a full 5-year warranty.  Please feel free to download details about the rebate as well as a letter that may be presented to your customers from the following webpage:

http://www.beaconpower.com/support/rebate.htm

In the future, please do not hesitate to contact me with any questions or concerns.

Kind regards,
Marko Rosenfeldt
Service Manager
Beacon Power Corp.
978-661-2024
rosenfeldt at beaconpower.com
www.beaconpower.com

-----Original Message-----
From: max [mailto:max at seesolar.com]
Sent: Tuesday, February 24, 2004 10:55 AM
To: RE-wrenches at topica.com
Subject: mm 5000 [RE-wrenches]


I have a customer with a mm 5000 that has died. I had to shut off the system
and bypass the feed to the emergency panel because the inverter would not
pass current through the contactor in the fault mode. The red light is
blinking, upon resetting, the green grid light comes on momentarily and then
the inverter starts blinking red and doesn't pass current through to the
emergency panel. The customer no longer has the manuals for the equipment
and I don't have a copy. All the array voltages and SC currents are as they
should be, and the battery bank appears in good condition - Does anybody
know if Beacon is supporting these machines - they don't return
calls..........Also where can I get a copy of the manual, or schematics???

Max Balchowsky
Solar Electric Energy Systems
100 S. Sunrise Wy #285
Palm Springs, Ca. 92262
Phone - 760-403-6810
Fax     -  760-406-4230


“Building a Lasting Future For the Next Generation�

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list