Inverter Monitoring & Canceling Meter Legs [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Tue Feb 17 10:52:37 EST 2004
Geoff at Third-Sun.com wrote:
> I did connect the little screw to a neutral wire (after removing the
> jumper) - some instructions I got told me to connect it to ground but I
> was thinking that - minute as it is - the micro motor load would be
> using the ground as a conductor. Am I right in this thinking and
> practice? If so we should heads up the suppliers who are recommending
> this practice.
Yes - the tap should be connected to the neutral - not ground - as there
will be a small ground fault current otherwise. Might be enough to trip
off bathroom GFCIs - but only if the meter was installed in certain
areas of the system which is not likely.
I think external CT meters will be the long term solution - just need
less expensive units with bi-directional capability.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list