Marco wrote:
> Anyone know whether 120 to 208/120 is possible with an off-the-shelf
> piece of hardware?
You can stack three OutBack FX series inverters into a three phase
configuration for 120/208 VAC "WYE" output (4 wire) with a HUB4 or
HUB10. The two slave inverters can even go into search mode when no
three phase loads are operating.
You can charge from either a single phase or three phase generator or
grid. The two phases not connected to the single phase AC source
continue to invert while the other phase charges - this allows single
phase power to be made into three phase power (although is a round about
manner).
Phase "C" can also have additional inverters connected in parallel for
higher output if a mixture of single and three phase loads are expected.
We will in the not so distant future be able to have more than one
inverter on phase A and B as well.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list