Doug Pratt wrote:
> Outback is working up a solution that might suit you Darryl, but it
> isn't available quite yet. I forget exactly what they're calling it,
> zero metering or something like that.
We are calling this our "ZERO" mode - because zero power is sold back to
the utility grid. You also can think of it as "ZEROING" out your
utility consumption - assuming you have enough RE source.
This is intended to be another choice for system configuration - Someone
at HomePower dubbed it "legal guerrilla solar" mode which describes it
fairly well. We use an additional current sense transformer located in
the main AC panel to sense the direction of the current flow. This CT
attaches to inverters "XCT" terminals that have always been there in all
the OutBack inverters... (but are not yet active).
We need to get a few of these systems installed and monitored before we
enable it in the grid-tie version code. One step at a time...
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list