SW stacking question [RE-wrenches]

Christopher Freitas --- OutBack Power cfreitas at outbackpower.com
Mon Jan 12 18:54:32 EST 2004


jay peltz wrote:
> Can I stack 2 Sw 2512's into a center taped 24v battery bank?

No - you cannot stack two 12 volt SW inverters for +/-12 vdc or 24 vdc 
system.  The interconnecting stacking cable is "ground" referenced (to 
the negative DC terminal of the inverter) which means that the signals 
would not be at the same level. You would fry the cable or the computer 
boards even...

It also would be easy to discharge the battery halves unequally since 
the inverters are powering separate loads.  

We did consider being able to do this with our OutBack inverters - but 
the amount of applications requiring this are pretty few...  

You might look at a dc-dc converter but for the cost you might consider 
upgrading the inverters to 24 vdc and selling the old ones off.  

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com  
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030  

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list