If you are using an Outback system, is there a reason you are installing a 
transfer switch? The capability is built into the Outback.

Regarding future utility feed to the site:  If you wish to run the entire 
400 amps through the transfer switch, then yes, it has to be rated for 400 
amps.  This scenario seems very unlikely, however.  My suggestions:

1. Skip the transfer switch for now.
2. If grid power will inevitably come to the site, leave physical space for 
the transfer switch and means to plumb it into the system.
3. When grid arrives, size the transfer switch to the critical loads plus 
some headroom for battery charging.  Feed it off the 400 amp main with a 
breaker sized for the transfer switch.  The remainder of the 400 amps can 
feed a non-critical load panel.
4. Place the critical and non-critical load centers next to each other with 
a generous nipple between them.  If the client changes their mind about 
what is critical and what is not, the branch circuits can easily be relocated.

I seem to recall Outback has some scheme to tell the inverters they are 
being fed by grid versus a generator.  Make sure you understand this 
completely.  I've not used this specific system yet.

Need more clarification or design help?  Contact me directly.

William Miller

At 10:58 AM 12/7/2004, you wrote:

>Hello
>
>
>
>Does anyone know the code issue for an off grid pv application. I have a
>system that is 7.7 KW with a 15 KW Coleman genny. What is the code
>requirement for the size of the ATS? Does it have to be 50 amps (15KW/120v)
>or does it need to be the max size of the combined output of the system-
>8-2500 watt Outback's (200 amp)?
>
>
>
>The other question arouse where we could in the future see the utility
>arrive at the site and this property was wired with the potential of 400
>amps. Does the ATS need to be 400 amp rated?
>
>
>
>Thanks!
>
>
>
>Keith Cronin
>
>President
>
>Island Energy Solutions Inc.
>
>270 Kuulei Rd Suite 106
>
>Kailua, HI 96734
>
>808-262-3268 Tel
>
>808-263-0338 Fax
>
>keith at islandenergy.net
>
>www.islandenergy.net
>
>  <http://www.islandenergy.net>
>
>
>
>
>
>  <http://www.islandenergy.net>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>[Non-text portions of this message have been removed]
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Are you serious about buying a NEW car or truck soon?
>Research before stepping on the car lot and save THOUSANDS!
>Get NO OBLIGATION price quotes from car dealers in your area.
>http://click.topica.com/caacVmkbz8QcsbAoCKvf/LeadClick
>-------------------------------------------------------------------
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Free recipes to get you in shape
http://click.topica.com/caacVmfbz8Qcsbz9JC9f/PermissionData
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>


More information about the RE-Wrenches mailing list