William,
The C40 is a PWM controller with no adjustment for turn on, turn off.
Inappropriate for driving a relay or any motor load. It should be
used for resistive loads only. You need a very simple voltage
controlled switch with adjustable on and off points to drive the
relay. If you are using an SW inverter, you've got it built in
already. If an SW+, buy the ALM module.
bob-O
>Friends:
>
>I am working on a system for load control in which the load is a 240
>well pump. It worked well for about a year using a Xantrex C40 to
>drive a two pole relay.
>
>About two months ago the client complained that the well would
>occasionally run until the battery V got low enough for the inverter
>to shut of. We could never observe this happening, but with my new
>data acquisition system, we recorded it doing this. The battery
>voltage went below the set point of 22 volts, but the C40 continued
>to drive the relay.
>
>I had another used C40 in the shop so I swapped them out. I
>recorded performance for another 24 hours and it worked well (excuse
>the pun) and I then removed the recording equipment.
>
>This morning I received a message from the client indicating the
>unit had yesterday again discharged the batteries. Unique to this
>situation is the fact that we had such a rainy day that I doubt the
>C40 reached the reconnect point.
>
>Have any of you used a C40 to control loads? to what success?
>
>Thanks,
>
>William Miller
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Get your Golden Tee CD ROM on us
http://click.topica.com/caacOlvbz8Qcsbz9JC9f/PermissionData
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list