Advanced PV Course [RE-wrenches]

David Palumbo, Independent Power & Light ipl at sover.net
Mon Oct 18 15:44:21 EDT 2004


 

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Like music? Get a CD Player here
http://click.topica.com/caacJzebz8Qcsbz9JC9a/PermissionData
-------------------------------------------------------------------

Bill,
Yes I would be interested in your advanced course. I'm sure it would give me
my continuing education component for NABCEP re-certification and update me
on all the latest install and trouble shooting techniques. I work in the
Northern part of Vermont, very rural, all off-grid installs. I have not done
a grid tie system since 2000. I'm sure that I will do more grid ties in the
future so this course would be ideal for me.

Best Regards,
David Palumbo
Independent Power
Hyde park, VT
NABCEP Certified Solar PV Installer
(802)-888-7194


-----Original Message-----
From: Bill Brooks [mailto:billb at endecon.com]
Sent: Monday, October 18, 2004 12:24 PM
To: RE-wrenches at topica.com
Subject: RE: Performance of Large Outback system [RE-wrenches]




Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Want to go on a Cruise for Free?
http://click.topica.com/caacIqObz8QcsbAlwJ5a/PermissionData
-------------------------------------------------------------------

Darryl, Matt, and Doug,

Where are your irradiance measurements? How do any of your output readings
have any meaning without an irradiance measurement? Do any of you own a
Daystar meter or do you have a spare module that you can get a Isc
measurement from? Carl brings an important point about temperature, but it
is a much lower order effect than irradiance. No power measurement should
even be written down without a corresponding irradiance measurement.

Forgive me for bringing up my pet peeve again, but I recently came from an
installation of one of the most knowledgeable installers in the state. The
array wasn't working well so they suggested removing the 3 C-40 charge
controllers and installing 3 MX-60 charge controllers in their place (a very
expensive proposition as you all know).

The problem had nothing to do with the C-40s. A quick check of the string
currents showed a 3:1 differential from the best string to the worst string.
As it turned out with further inspection (with a $21K Daystar curve tracer
that I don't expect anyone to own), that every single string had failed
modules. The array will be replaced, but the sad thing is that this "very
knowledgeable" installer could not tell that the array was a total mess and
suggested a fix that did absolutely no good.

My plans are to design an advance PV Design, Installation, and
Troubleshooting course. Is there any interest from current installers? I've
been working with grid-connected systems for over 16 years now, and I'm
learning new things every single day.

Understand that I am not trying to be patronizing about this--I'm just
trying to get installers to do things properly so that they can be confident
with the results of any measurements they make on their systems. Please go
back and send some information on performance that is related to irradiance
and temperature.  I'm sure everyone on the list is interested in informative
results.

Bill.

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Like music? Get a CD Player here
http://click.topica.com/caacJzebz8QcsbAlwJ5f/PermissionData
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Click here for your Golden Tee CD ROM
http://click.topica.com/caacJzobz8Qcsbz9JC9f/PermissionData
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------









More information about the RE-Wrenches mailing list