Xantrex response SW+ [RE-wrenches]

Ray Walters ray at solarray.com
Fri Sep 3 15:47:49 EDT 2004


<x-flowed>
 

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Amazing Diet Patch
The fastest - Easiest way to lose weight! Try it now FREE!
http://click.topica.com/caacBBBbz8Qcsbz9JC9a/MyDietPatches
-------------------------------------------------------------------

Hi Mark;

Thanks for the quick response. The Staber (measured with a "Brand" watt 
meter was peaking around 1500 VA, this is a fairly slow response meter 
though, so the instantaneous draw may be much higher)
Further testing was done with a worm drive circular saw. The continuous 
draw of the saw was around 1000 watts, the surge current (as seen on the 
SW+ meter menu) was 27 amps AC. A quick capture of DC current through the 
shunt showed a 1/10 sec surge of 175 amps. DC volts at the shunt would drop 
from 24.6 (rest) to 22.9vdc (1/10 sec minimum). I measured 0.3 vdc line 
loss (under 2%) from the batteries to the shunt, and again that was just 
for a  1/10 sec surge.
  So basically you're saying that on a startup surge that exceeds 2500 
watts, voltage regulation is out. I could see it relaxing to say 10%, but 
86 vac is over 25% out. Is there anyway to tighten the regulation (and 
probably reduce the surge capability)? The high surge is nice compared to 
the original SW series, but in this case we're paying the price in power 
quality. Is this a smaller transformer, and therefore a higher impedance 
issue? None of my measurements are showing more than a 4000 watt surge (and 
that one is figured at the DC input, not output)
Do I need to go get a Fluke 43, so I can get a more instantaneous power 
factor reading too? (I'm just itching to get one, but I'd probably annoy 
the list even more then)
I am about to head out there, let me know if there is anything I should be 
looking for.

Ray

>Hi Ray,
>
>The 2548+ is rated to provide the nominal output (120Vac +/- 3%) up to a
>load of 2500 VA - with surges substantially above this the voltage will
>droop outside the regulation window. Do you know how much current the
>Staber was drawing at start up?
>
>Regards,
>
>Mark Edmunds
>Xantrex Technology
>
>
>Solar Ray wrote:
> >
> > Hi Mark;
> >
> > I'm glad to see you on the list. I really never got a response from you
> > though on the SW+ voltage sag issue. ( it was a string you may have
> > missed
> > a couple of weeks ago) I will summarize: basically I and other wrenches
> > have noticed SW+ voltage output dipping below 100 vac during inductive
> > load
> > starting. This is accompanied by the various expected symptoms of a
> > brown
> > out, i.e. lights flickering , computer UPS beeping on, etc.
> > In my case, we have a malfunctioning Staber washing machine that we have
> >
> > gone through 2 replacement control boards. Staber insists it is a power
> > quality issue. I was really fending for the SW+, until I set my Fluke89
> > to
> > regular minimum capture and found the voltage dropping to 86 vac for
> > about
> > a tenth of a second, while starting a circular saw. I checked DC wiring
> > and
> > connections, volt drop between the batteries and inverter, AC wiring
> > ,etc.
> > I have come to the current conclusion that the new SW+ series allows the
> >
> > voltage to dip on purpose to achieve its 10,000 watt surge rating. BTW,
> > I
> > have seen these same symptoms on 3 different units, both the SW2524+,
> > and
> > the SW2548+.
> >
>
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Save on inkjet and toner, and get free shipping on orders over $50.
>http://click.topica.com/caacBBybz8QcsbeuiVOf/Inksoutlet
>-------------------------------------------------------------------
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com

Ray Walters
ray at solarray.com
President, SolarRay, Inc.
NABCEP Certified Solar PV Installer
BS Mechanical Engineering, UT Austin 88
Returned US Peace Corps Volunteer 

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Save up to 67% on Omaha Steaks + Get 6 FREE Burgers and a 
FREE Cutlery Set + Cutting Board!
http://click.topica.com/caacBBEbz8Qcsbz9JC9f/OmahaSteaks
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>


More information about the RE-Wrenches mailing list