Flexible Cables: Important Safety Issue [RE-wrenches]

Matt Tritt solarone at charter.net
Thu Aug 26 23:47:02 EDT 2004


 

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Save up to 80% on Inkjet & Toner Supplies. 100% Satisfaction 
Guarantee. Free Shipping on orders over $49. www.inksoutlet.com
http://click.topica.com/caacAsfbz8Qcsbz9JC9a/Inksoutlet
-------------------------------------------------------------------

  Hi Kurt,

  Yep, that sounds right to me. As far as crimp lugs go, I've always (well,
maybe not always) used the heavy Magna lugs with three crimps. I got the
crimper years ago from Dave Katz at AEE; one of my favorite tools. Even
though  there are some wire sizes and types that are a real booger to get
into the fittings, particularly the 2/0 welding cable with the 10 zillion
strands, when those babies are crimped - they stay crimped. Not even J.
Wiles could pull 'em out! Maybe.

  Matt T

  ----- Original Message ----- 
  From: "Kurt Nelson" <sunwise at cheqnet.net>
  To: <RE-wrenches at topica.com>
  Sent: Thursday, August 26, 2004 7:34 PM
  Subject: RE: Flexible Cables: Important Safety Issue [RE-wrenches]




  Your free subscription is supported by today's sponsor:
  -------------------------------------------------------------------
  Save up to 80% on Inkjet & Toner Supplies. 100% Satisfaction
  Guarantee. Free Shipping on orders over $49. www.inksoutlet.com
  http://click.topica.com/caacAsfbz8QcsbadqCja/Inksoutlet
  -------------------------------------------------------------------

  Hey Matt,

  I have not yet read all the posts on this topic, but let me quickly say
  two things.  First, I thought JW was commenting on both crimped
  connections and connections under a screw.

  Second, I have always placed two dabs of No-Ox on at such connections,
  one little line along the threads of the screw and another big dab at
  the front, compression end of the screw.

  I was told that the proper way to tighten these was to reef on the
  t-handled allen wrench, but then back off and re-tighten, repeating a
  few times.  The last time the screw is tightened there is no additional
  compression noticed at the tool and it is not necessary to over tighten.

  Kurt Nelson


  -----Original Message-----
  From: Matt Tritt [mailto:solarone at charter.net]
  Sent: Thursday, August 26, 2004 11:10 AM
  To: RE-wrenches at topica.com
  Subject: Re: Flexible Cables: Important Safety Issue [RE-wrenches]



  Your free subscription is supported by today's sponsor:
  -------------------------------------------------------------------
  Save up to 80% on Inkjet & Toner Supplies. 100% Satisfaction
  Guarantee. Free Shipping on orders over $49. www.inksoutlet.com
  http://click.topica.com/caacAsfbz8QcsbAsGU2a/Inksoutlet
  -------------------------------------------------------------------

    Kurt,

    Even though I find it gratifying to solder cable lugs, the real
  subject of
  J. Wiles ridiculous suggestion/RULE  is the wire or cable that is
  terminated
  under a screw or clamp. His "concern" for this connection is that the
  fine
  wire strands will somehow break in the process of tightening the screw
  (or
  that it will just keep compressing after it has been completely
  compressed
  to begin with) resulting in reduced current carrying ability; hence my
  tinned cable end reference. See Don's comments on tightening the screw
  after
  inserting the cable. Better yet, go back to the original message
  conduited
  through A. Sindelar if you really feel like getting steamed!

    Wiles makes a comment about a "recent problem" with a "large PV
  system"
  resulting from a loose connection that had been "re-torqued" a short
  time
  before the Problem occured. The thing that is the biggest pisser about
  Wiles
  and his cohorts of the meddling persuasion is that this ambigous
  "problem"
  occurance is turning into a new (and preposterous) rule that will effect
  a
  huge portion of the industry, from module and inverter manufacturers
  clear
  down to the guys in the field, and like Bob-O says; the result will be
  higher prices for all.


    I completely agree with you about Bob-O; I sure hope the men in the
  (UL
  approved) black helicopters don't whisk him away in the night!

    Matt T
    ----- Original Message ----- 
    From: "Kurt Nelson" <sunwise at cheqnet.net>
    To: <RE-wrenches at topica.com>
    Sent: Thursday, August 26, 2004 6:50 AM
    Subject: RE: Flexible Cables: Important Safety Issue [RE-wrenches]




    Your free subscription is supported by today's sponsor:
    -------------------------------------------------------------------
    Save up to 80% on Inkjet & Toner Supplies. 100% Satisfaction
    Guarantee. Free Shipping on orders over $49. www.inksoutlet.com
    http://click.topica.com/caacAsfbz8QcsbadqCja/Inksoutlet
    -------------------------------------------------------------------

    Hey Bob-O,

    Regarding crimp/solder lugs, I used to do a "primitive" crimp on the
    lugs and then heat the lug and fill with solder.  I've heard that a
    properly crimped connection actually has less resistance than a
  soldered
    one (maybe those solder'ers aren't also crimping?).  A couple years
  ago
    I bought the big/proper crimping tool.  It is really quick and easy.
    Yet I often walk away from a job thinking that maybe I should have
  added
    solder to the lug, to make it a permanent connection.

    All that said, What I really wanted to say was that when it comes to
    these Wrenches posts, and having recently been watching some of the
    Olympics, I am a big fan of Bob-O's style and form.

    Kurt Nelson
    SOLutions

    -----Original Message-----
    From: Bob-O Schultze, Electron Connection
    [mailto:econnect at snowcrest.net]
    Sent: Wednesday, August 25, 2004 10:29 AM
    To: RE-wrenches at topica.com
    Subject: Re: Flexible Cables: Important Safety Issue [RE-wrenches]



    Your free subscription is supported by today's sponsor:
    -------------------------------------------------------------------
    Buy Stocks and Index Funds for just $4 No Account or
    Investment Minimums and No Inactivity Fees Automatically
    invest weekly or monthly and build your future.
    http://click.topica.com/caacvggbz8QcsbAsGU2a/Sharebuilder
    -------------------------------------------------------------------

    Well, that's old JW all over isn't it? Find a situation that could be
    a problem or that is very, very rarely a problem and make Mt Everest
    out of a molehill. Since day one of his inputs to the RE industry
    everything he suggests or opines that UL/NEC requires raises the cost
    of a PV system. EVERYTHING! Ever notice that? This man comes to us
    from the nuke industry. I find it damn hard not to question his
    motives. He's kind of a Swift Boat PV Opinionater for Arcane Stuff,
    ain't he?
    Jesus H. Christ!


    >  Oh my God.
    >
    >   This isn't April 1st is it?
    >
    >   So now all those inverters that we've been putting in with "fine
    stranded
    >wire" for the past 20 years are going to have to have their cables
    removed
    >and exchanged because "there have been problems"? What, fires?
    Explosions?
    >Electrocutions? Befuddled inspectors?
    >
    >   I have to say that in all the years I've been working on
    battery-based
    >inverters, the ONLY connection problems I have observed  have ONLY
  been
    >those that had stiffy wire for inverter cables! There is so much
    potential
    >for tension-caused breakage with this method, so many (virtually)
    impossible
    >wire bends and seeming non-compatablity with all the commonly used,
    tried
    >and true connection components, I just can't bel;ieve that this can
  be
    for
    >real.
    >
    >   If this such a huge problem, why not simply tin the wire ends?! UL
    indeed.
    >
    >   Matt T
    >   ----- Original Message -----
    >   From: "Allan Sindelar" <allan at positiveenergysolar.com>
    >   To: "New wrenches posting" <RE-wrenches at topica.com>
    >   Sent: Tuesday, August 24, 2004 3:35 PM
    >   Subject: Fw: Flexible Cables: Important Safety Issue [RE-wrenches]
    >  Wrenches,
    >   Forwarded to this list at the request of John Wiles
    >
    >   ----- Original Message -----
    >   From: "John Wiles" <jwiles at nmsu.edu>
    >   Sent: Tuesday, August 24, 2004 3:50 PM
    >   Subject: Flexible Cables
    >
    >
    >   Flexible, Fine-Stranded Cables: Incompatibilities with Set-Screw
    >Mechanical
    >   Terminals and Lugs
    >
    >   Reports have been received over the last several years about
    field-made
    >   connections that have failed when flexible, fine-stranded cables
    have been
    >   used with mechanical terminals or lugs that use a set screw to
  hold
    the
    >wire
    >   in the terminal.
    >
    >   These terminals are found on nearly all circuit breakers (except
    those
    >with
    >   stud-type terminals), fuse holders, disconnects, PV inverters,
    charge
    >   controllers, power distribution blocks, some PV modules, and many
    other
    >   types of electrical equipment.
    >
    >   Fine-stranded conductors and cables are considered as those cables
    having
    >   stranding more numerous than Class B or C stranding. Class B
    stranding
    >(the
    >   most common) will normally have 7 strands of wire per conductor in
    sizes
    >   18-2 AWG, 19 strands in sizes 1-4/0 AWG, and 37 strands in sizes
    250-500
    >   kcmil. Conductors having more strands than these are widely
    available and
    >   are in different classes such as K and M used for portable power
    cords and
    >   welding cables. Commonly used building-wire cables such as USE,
  THW,
    RHW,
    >   THHN and the like are most commonly available with Class B
    stranding, but
    >   are also readily available with higher stranding. Fine-stranded
    cables are
    >   frequently used by PV installers to ease installation and are used
    in PV
    >   systems for battery cables, power conductors to large
    utility-interactive
    >   inverters and elsewhere.
    >
    >   Some modules are supplied with fine-stranded interconnecting
  cables
    with
    >   attached connectors. While these crimped-on connectors listed with
    the
    >   module are suitable for use with the fine-stranded conductors, an
    >   end-of-string conductor with mating connector may also be supplied
    with
    >the
    >   fine-stranded conductor ,and the unterminated end of that
  conductor
    will
    >not
    >   be compatible with mechanical terminals.
    >
    >   According to UL Standard 486 A-B, a terminal/lug/connector must be
    listed
    >   and marked for use with conductors stranded in other than Class B
    and C.
    >   With no marking or factory literature/instructions to the
  contrary,
    the
    >   terminal may only be used with conductors with the most common
  Class
    B and
    >C
    >   stranded conductors. They are not suitable and should not be used
    with
    >   fine-stranded cables. UL engineers have said that few (if any) of
    the
    >normal
    >   screw-type mechanical terminals that the PV industry commonly uses
    have
    >been
    >   listed for use with fine stranded wires. The terminal must be
  marked
    or
    >   labeled specifically for use with fine-stranded conductors.
    >
    >   UL suggests two problems, both of which have been experienced in
  PV
    >systems.
    >   First, the turning screw tends to break the fine wire strands,
    reducing
    >the
    >   amount of copper available to meet the listed ampacity. Secondly,
    the
    >   initial torque setting does not hold and the fine strands continue
    to
    >   compress after the initial tightening. Even after subsequent
    retorquing,
    >the
    >   connection may still loosen. The loosening connection creates a
    >   higher-than-normal resistance connection that heats and may
    eventually
    >fail.
    >   Recent examples of failed mechanical terminals from a large PV
    system have
    >   been found. The terminal had been torqued properly less than three
    months
    >   before the failure.
    >
    >   Solutions
    >
    >   All electrical equipment listed to UL Standards has:
    >
    >   . Terminals rated for the required current and sized to accept the
    proper
    >   conductors
    >
    >   . Sufficient wire bending space to accommodate the Class B
  stranded
    >   conductors in a manner that meets the wire bending requirements of
    the NEC
    >
    >   . Provisions to accept the appropriate conduit size for these
    conductors
    >   where conduit is required.
    >
    >   It is therefore unnecessary to use the fine-stranded cables except
    >possibly
    >   when dealing with conductors 4/0 AWG and larger.
    >
    >   In those cases where a fine-stranded cable must be used, a few
    >manufacturers
    >   make a limited number of crimp-on compression lugs in various
  sizes
    that
    >are
    >   suitable for use with fine-stranded cables.
    >
    >   Factory-supplied markings and literature indicate which lugs are
    suitable.
    >   An example is the ILSCO FE series of lugs in sizes 2/0 AWG and
    larger.
    >   Burndy makes a YA series of lugs in sizes 14 AWG and up. In both
    cases the
    >   lugs are solid copper. It should be emphasized: Most crimp-on lugs
    are not
    >   listed for use with fine-stranded wire. Where the crimp-on
    compression
    >lugs
    >   can be used, they must be installed using the tools recommended by
    the
    >   manufacturer and, of course, they must be attached to a stud with
  a
    nut
    >and
    >   washer.
    >
    >   Burndy and others make pin adapters (a.k.a. pigtail adapters) that
    can be
    >   crimped on fine-stranded cables. These pin adapters provide a
    protruding
    >pin
    >   that can be inserted into a standard screw-type mechanical
    connector.
    >Again,
    >   not all pin adapters/pigtail adapters are listed for use with
    >fine-stranded
    >   conductors; some are intended for use with aluminum wire and
  others
    >provide
    >   only a conversion to a smaller AWG size for B Class conductor.
    >
    >   It is suggested that the use of fine-stranded conductors be
  avoided
    >wherever
    >   possible. Where such cables must be used, they should only be
    terminated
    >   with the appropriate connectors/lugs. Previously installed systems
    should
    >be
    >   revisited and the cables replaced where possible or terminated
    properly.
    >
    >   John Wiles SWTDI/NMSU jwiles at nmsu.edu 505-646-6105
    >
    >   > If I can provide further information, please do not hesitate to
    call,
    >   > e-mail or fax me.
    >   >
    >   > John
    >   >
    >   > John C. Wiles,  Program Manager
    >   > Southwest Technology Development Institute, New Mexico State
    University
    >   > 505-646-6105      505-646-3841 (FAX)   http://www.NMSU.Edu/~tdi
    >   > SWTDI/NMSU
    >   > Corner Research Drive and Sam Steel Way
    >   > Box 30001/MSC 3 SOLAR
    >   > Las Cruces, NM 88003-8001
    >

    Your free subscription is supported by today's sponsor:
    -------------------------------------------------------------------
    RE-GROW YOUR HAIR STARTING NOW.....Click here for more info!
    http://click.topica.com/caacxydbz8QcsbAsGU2f/Medical Hair Restoration
    -------------------------------------------------------------------

    - - - -
    To send a message: RE-wrenches at topica.com

    Archive of previous messages:
    http://lists.topica.com/lists/RE-wrenches/read

    List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

    Check out participant bios: www.mrsharkey.com/wrenches/

    Hosted by Home Power magazine

    Moderator: michael.welch at homepower.com

    Your free subscription is supported by today's sponsor:
    -------------------------------------------------------------------
    RE-GROW YOUR HAIR STARTING NOW.....Click here for more info!
    http://click.topica.com/caacxydbz8QcsbadqCjf/Medical Hair Restoration
    -------------------------------------------------------------------

    - - - -
    To send a message: RE-wrenches at topica.com

    Archive of previous messages:
  http://lists.topica.com/lists/RE-wrenches/read

    List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

    Check out participant bios: www.mrsharkey.com/wrenches/

    Hosted by Home Power magazine

    Moderator: michael.welch at homepower.com

  Your free subscription is supported by today's sponsor:
  -------------------------------------------------------------------
  Buy Stocks and Index Funds for just $4 No Account or
  Investment Minimums and No Inactivity Fees Automatically
  invest weekly or monthly and build your future.
  http://click.topica.com/caacvggbz8QcsbAsGU2f/Sharebuilder
  -------------------------------------------------------------------

  - - - -
  To send a message: RE-wrenches at topica.com

  Archive of previous messages:
  http://lists.topica.com/lists/RE-wrenches/read

  List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

  Check out participant bios: www.mrsharkey.com/wrenches/

  Hosted by Home Power magazine

  Moderator: michael.welch at homepower.com

  Your free subscription is supported by today's sponsor:
  -------------------------------------------------------------------
  Need cash fast? Get a $500 CASH ADVANCE overnight! Let
  YourCashCentral get you the cash you need.
  http://click.topica.com/caacxycbz8QcsbadqCjf/MyOnlinePayday
  -------------------------------------------------------------------

  - - - -
  To send a message: RE-wrenches at topica.com

  Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read

  List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

  Check out participant bios: www.mrsharkey.com/wrenches/

  Hosted by Home Power magazine

  Moderator: michael.welch at homepower.com

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Stories from the Civil Rights Movement. Extraordinary stories, 
ordinary people. Share your memories today!
http://click.topica.com/caacvglbz8Qcsbz9JC9f/AARP
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------

















More information about the RE-Wrenches mailing list